Electric Thermal Relay

01/13/2016 9:48 AM

What is the rating or ampere of thermal overload relay to protect 35kw of electric motor(3phase)?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#1

Re: electric thermal relay

01/13/2016 9:51 AM

Check the nameplate and applied voltage and current tag on the motor.

__________________
Plenty of room here
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: electric thermal relay

01/13/2016 9:52 AM

That depends on a lot of things. From the sparse amount of information you give us, I doubt you'd understand what needs to be known.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: electric thermal relay

01/13/2016 10:18 AM

The rating or ampere of thermal overload relay should be low enough to protect the wiring, but not so low as to hinder operation of the motor, if properly sized and installed.

As already mentioned, you will need to find a competent local electrician to enlighten you.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: electric thermal relay

01/13/2016 10:29 AM

The OCPD protects the cable and starter, the thermal relay the motor.

You can get combined units from some manufacturers.

Set the relay to the value on the motor rating plate, better still get a qualified electrician to do it for you.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5

Re: electric thermal relay

01/13/2016 11:05 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#6

Re: Electric Thermal Relay

01/13/2016 1:00 PM

P=I*E

You gave us the P, want to know the I and didn't think or know that we need the E.

I say your over your head so call an electrician.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: Electric Thermal Relay

01/13/2016 1:20 PM

There is only one answer, already given. You MUST read the motor nameplate full load amps, then select or adjust the OL heater element or dial adjustment as per the instructions provided by the manufacturer. There is no other accurate method of accomplishing proper motor protection, everything else is just a guess, and guessing is for gamblers, not engineers.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Electric Thermal Relay

01/13/2016 7:23 PM

The protocol is in British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#9
In reply to #8

Re: Electric Thermal Relay

01/14/2016 7:25 AM

Try

BS 4941
BS-EN 60947
IEC 292
IEC 947.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
2
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#10

Re: Electric Thermal Relay

01/14/2016 8:46 AM

Look at the full load amps on the data plate, (FLA) on the motor.

Multiply this value by the service factor (SF), usually 1.25.

Then look up the value on the chart that applies to the motor starter contractor for the appropriate heater number.

There will usually be a chart on the inside cover of the enclosure of the starter.

There are also factors for a variable ambient temperature to consider.

These numbers will vary from one brand of contractor to another: Furnas, Westinghouse, Square D, GE, ITE, Siemens, etc.

I am presuming that you have the proper sized motor contactor for the motor in question.

This is about a 47 to 50 hp motor, so the starter size could range from a NEMA size 4 to a NEMA size 5, depending on the voltage and RPM of the motor.

I will not help you calculate the proper wire size and short circuit protection for this circuit.

If you cannot do that, turn the job over to a qualified electrician, which is a good idea anyway.

Remember the old saying among electricians:

There are Old Electricians, and there are Bold electricians, but there are No Old, Bold Electricians.

Work safely.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Good Answer (Score 2)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#11

Re: Electric Thermal Relay

01/15/2016 9:46 PM

1) Is it a European (IEC) or North American (NEMA) motor? NEMA motors have a service factor, already comprehensively covered.

2) Is it a DOL starter? Or is it a star-delta starter with the relay within the delta? The setting in this case will be 1/√3 of the rated current.

Easier to look at the manufacturer's recommendation from the catalogue - here is one example from Schneider Electric :

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#12

Re: Electric Thermal Relay

01/16/2016 11:11 AM

My guess based on the 35kW description would be an IEC motor. So no Service Factor involved. We don't use kW for mechanical power here, we use Horsepower, because horses were here first (James Watt rode one!) and are cuter than James Watt was (or so I'm told).

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#13

Re: Electric Thermal Relay

01/18/2016 3:10 AM

Giving a simple question as "What is the rating or ampere of thermal overload relay to protect 35kw of electric motor(3phase)?" is a job of non electrical personal. As an electrician personal they will also include other data's like the "rated voltage" and "rated frequency" so that calculation can be done with all these data's.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Participant

Join Date: Jan 2016
Posts: 3
#14

Re: Electric Thermal Relay

01/18/2016 4:21 AM

The setting within 125 percent of rated current and time dial could set to min sellection

Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

dvmdsc (1); HiTekRedNek (1); JRaef (2); kvsridhar (1); lyn (1); ozzb (1); PWSlack (1); redfred (1); Simon Wan (1); SolarEagle (1); TonyS (2); yasser adham (1)

Previous in Forum: Know What I Need, Don't Know What To Call It.   Next in Forum: Heating Steel

Advertisement