Ultersonic Flowmeter 91W

01/17/2016 12:44 PM

Dear All

I have installed a flow meter on horizontal on the pipe, there is a signal for two sensors but there is no flow reading, I am wondering what is the reason, please can anyone help me about this issue and please provide me how many ways for installtion

Register to Reply
This discussion was "closed" on 01/17/2016 7:51 PM. No new comments are allowed.
Message from admins:
Duplicate thread. See other thread at: http://cr4.globalspec.com/thread/105549
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: ultersoic flowmeter 91w

01/17/2016 1:55 PM

Aboosh,

We cannot read your mind to know what has been done.We cannot see the installation to know how it was done.You do not provide any useful information that could be used to help you.

CONTACT YOUR SUPPLIER and ask them for help.

Perform a search to find a troubleshooting guide FOR YOUR INSTRUMENT. Then follow the instructions you will find there.If all else fails, call a technician.

You claim to be an electrical engineer, figure it out!

You might draw some inspiration from this :

Positively Good Productions

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: ultersoic flowmeter 91w

01/17/2016 2:26 PM

<unsubscribe>

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: ultersoic flowmeter 91w

01/17/2016 3:38 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#4

Re: ultersoic flowmeter 91w

01/17/2016 6:14 PM

Transit time ultrasonic clamp-on flow meter: Failure to get a flow signal

1. Misplaced receiver transducer - outside the physical location for given fluid's sonic velocity and pipe size/material.

2. transducer cable or cable connector problem

3. Missing or insufficient pipe-to-transducer coupling compound (grease) or insufficient transducer-to-pipe coupling pressure

4. Poor exterior pipe condition - dirt, rust, loose paint

5. Scale or deposits inside the pipe wall attenuate the signal.

6. Entrained air, gas, bubbles or suspended solids attenuate the transit time signal.

7. High fluid velocity sweeps the acoustic signal past the receiver transducer.

8. Interference from ultrasonic 'noise' downstream of a valve (David Spitzer, http://www.flowcontrolnetwork.com/downstream-disturbances/

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: ultersoic flowmeter 91w

01/17/2016 7:44 PM

This is what happens when you not only throw away the manual, but also the box; then you can't even spell the name of the device properly.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Register to Reply 5 comments
This discussion was "closed" on 01/17/2016 7:51 PM. No new comments are allowed.