1000KVA Transformer: Unusual sounds

02/25/2016 1:15 PM

We have a 1000 KVA 11kv/420v 3p oil filled transformer in our facility to run a Hydrogen Production Electrolyzer. Its an old transformer with 750A load on it. But all of the tests were performed on it regarding insulation and oil before putting load on it.

Recently it has been malfucntioning and it tripped the HT supply.

problem # 01: Unusual vibrating sounds (apart from the usual buzzing and humming sounds due to magnetostriction)

problem #02: Sudden leakage of oil from the HV side bushings

Any thoughts on the issue?

__________________
Work until your idols become your rivals
Register to Reply
Pathfinder Tags: Electrolyzer transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: 1000KVA Transformer: Unusual sounds

02/25/2016 1:40 PM

Cracked HV insulator perhaps. Does it appear one or more of the HV insulators is under mechanical strain?

What's the oil level like now its operating, you say its leaking but is it getting low enough to expose internal connections that could be resulting in arcing and subsequent tripping? I believe a dissolved gas analysis of the oil now it has been operating and tripping in this way should pick up if it is tripping because of internal arcing.

With regard to the oil leakage, perhaps the old transformer just has some perished HV bushing seals and the real problem of the reason for tripping is elsewhere in the transformer.

__________________
jack of all trades
Register to Reply
Participant

Join Date: Feb 2016
Location: Pakistan
Posts: 4
#4
In reply to #1

Re: 1000KVA Transformer: Unusual sounds

02/26/2016 9:08 AM

HV insulators are perfectly intact and under no mechanical strain.

Oil level has dropped but not enough to allegedly expose internal connections.

Oil sample for DGA has been sent to the laboratory.

Bushing seals might be a problem, I'll get them replaced after inspection.

Thanks for the insight.

__________________
Work until your idols become your rivals
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: 1000KVA Transformer: Unusual sounds

02/25/2016 4:46 PM

Yes. Replace it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: 1000KVA Transformer: Unusual sounds

02/25/2016 6:01 PM

Transformers don't malfunction, they fail, "...it tripped the HT supply...", on what, overcurrent, overload, differential, etc.? As previously stated, do a DGA (Dissolved Gas Analysis) on it for a clue on what's happening inside. Unusual buzzing could be as simple as a loose mounting bolt, or as complex as intermittent arcing; you should also see if the something has changed in the load such as unusual current spikes, increasing THC/D (Total Harmonic Content/Distortion), etc.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Participant

Join Date: Feb 2016
Location: Pakistan
Posts: 4
#5
In reply to #3

Re: 1000KVA Transformer: Unusual sounds

02/26/2016 9:21 AM

Surprisingly, it malfunctioned. It still runs fine under load. I put it on a test run for 30 minutes, attached to a different load.

Yes, I have sent the oil sample for DGA, I just wanted to have a look at the possible causes of the failure/malfunction till I get back the results.

Nothing changed in load i.e., Electrolyzer. But electrolyzer is turned on and off on a regular basis. Maybe the startup causes some unusual current spikes, but I don't think I have any possible way to look at it, now that the transformer's been malfunctioning.

Thanks for your insight.

__________________
Work until your idols become your rivals
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: 1000KVA Transformer: Unusual sounds

02/26/2016 9:56 AM

RAM has asked now I'll ask "what did the 11kV trip on?"
What protection is fitted?
"Oil level has dropped but not enough to allegedly expose internal connections" is there no sight glass?
Have you replenished the oil? I think it's safe to assume no buchholtz unit is fitted.
Are the 11kV terminals in open air or in a compound filled box? If in compound oil leaking in to it will cause problems.

Try and answer the above questions and we may be able to help.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Participant

Join Date: Mar 2016
Posts: 1
#7

Re: 1000KVA Transformer: Unusual sounds

03/12/2016 1:41 PM

Better do the oil test...maybe the insulation in oil very low...

Register to Reply
Member

Join Date: Aug 2015
Posts: 9
#8

Re: 1000KVA Transformer: Unusual sounds

03/14/2016 3:03 AM

Electrical Transformers are most likely to a nested integral mesh box.They change 'Colors ' when temperature changes.Nuisance trip may occurs when a piece of undetected winding fault of turn - turn short that works to trip.Causing sounds are premature or tendency of pd.I think some arcing pockets can't reach up to relay by some restrictions .I suggest you to test the Transformer with 'Transformer Turn Ratio Tester ',then you will find any incredible fault. As you mentioned oil leaks to HT bushings at an instant is a 'weeping' of ageing gaskets . * Drilling of a water well is a great challange for driller. * Diagnostic fault finding of a Electrical Transformer also has the same meaning! Good Luck.

Register to Reply Off Topic (Score 5)
Register to Reply 8 comments
Copy to Clipboard

Users who posted comments:

ahmadtouqir (2); jack of all trades (1); Khinzawmyint (1); Muhamad fitry (1); PWSlack (1); RAMConsult (1); TonyS (1)

Previous in Forum: Battery Charger - 3 Ph Rectifier High voltage output   Next in Forum: Reactor Start

Advertisement