Is differential protection relay operates for open circuit in any one of transformer winding? Explain

__________________
Thanks and Regards, Sathish...
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Transformer Differential protection relay

03/05/2016 8:22 AM

Do your own homework

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Mar 2011
Location: Karnataka, India
Posts: 30
#3
In reply to #1

Re: Transformer Differential protection relay

03/05/2016 12:27 PM

Dear Sir,

As per my homework, relay will not operate.

Is it right or wrong?

__________________
Thanks and Regards, Sathish...
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Transformer Differential protection relay

03/05/2016 9:05 AM

Basic interview question, how did you respond?

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Associate

Join Date: Mar 2011
Location: Karnataka, India
Posts: 30
#4
In reply to #2

Re: Transformer Differential protection relay

03/05/2016 12:31 PM

Dear RAMConsult,

As per me it will not operate. Is it right?

__________________
Thanks and Regards, Sathish...
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6
In reply to #4

Re: Transformer Differential protection relay

03/15/2016 6:28 PM

Correct. Now can you tell me why?

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Associate

Join Date: Mar 2011
Location: Karnataka, India
Posts: 30
#7
In reply to #6

Re: Transformer Differential protection relay

03/18/2016 6:42 AM

If open circuit in any one winding, then the current in primary and secondary of the same phase will be zero. So there will be no difference of current in the same phase of primary and secondary. So in this case the differential relay will not operate.

right..??

__________________
Thanks and Regards, Sathish...
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8
In reply to #7

Re: Transformer Differential protection relay

03/18/2016 10:01 AM

Correct, as long as the sum of the currents going in equals the sum of the currents going out then the relay should not operate.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Associate

Join Date: Mar 2011
Location: Karnataka, India
Posts: 30
#9
In reply to #8

Re: Transformer Differential protection relay

03/19/2016 1:44 AM

Thank You...

__________________
Thanks and Regards, Sathish...
Register to Reply
Active Contributor

Join Date: Jun 2011
Location: Lucknow , Uttar Pradesh , India
Posts: 15
#5

Re: Transformer Differential Protection Relay

03/14/2016 1:43 PM

relay will be operate by my idea because relay work on current difference. if winding open than current value will be diffrent in each phase so relay will be work.

thanks

__________________
Mukesh Kumar
Register to Reply
Active Contributor

Join Date: Jun 2014
Location: South Korea
Posts: 18
#10

Re: Transformer Differential Protection Relay

04/07/2016 2:26 AM

Differential protection is operated with current. Without path (open CCT), no currents. We need to make path for electrons.

Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

moons (1); mukeshkumar5609 (1); RAMConsult (3); satishhar (4); TonyS (1)

Previous in Forum: Problems Faced in VT Ratio Test   Next in Forum: Numerical Over Current and Earth Fault Relay

Advertisement