High No-Load Current on Transformers

03/15/2016 1:42 AM

Dear Experts

I am failing to get a solution/ Explanation regarding this scenario. We manufacture Distribution and Power Transformers, Mostly all our transformers during No-load test the current is below 5% of the rated. Only in cases of small size Transformers you see the %ge going as high as +6%. On 3MVA 33/0.4kV or 11/0.4kV Dyn11 transformer the no-load currents are below 1% mostly even 0.6%. However when we do 3mVA, 2,5MVA or any other rating with voltage ratio of 11/33kV Step-up or 33/11kV the no-load currents are above 26%. Have referenced with previously done designs and they have all been tested as btwn 25 - 27%. Now we have a customer who is argueing that the no-load should be below 5%. Checked IEC it says the no-load current should be within +30% of design value. Why are we getting high no-load currents on 33/11 and 11/33kV Transformers ??? Please assist if you have faced this problem or have the know how.

__________________
"Do not follow where the path may lead. Go instead where there is no path and leave a trail."
Register to Reply
Pathfinder Tags: High No Load on Transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#1

Re: High No-Load Current on Transformers

03/15/2016 2:41 AM

What is the bases for the 100%?

__________________
Common Sense Dictates
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#2

Re: High No-Load Current on Transformers

03/15/2016 2:44 AM

No load currents are typically non-sinusoidal and full of harmonics.

Any internal fault will greatly amplify those harmonics with an increase in no load current.

A primary winding fault will generally increase total harmonic distortion (THD) and increase the value of no load current.

A secondary fault will just increase no load current.

A core fault will generally increase THD of the output with no corresponding increase in no load current.

Surely a manufacturer of such equipment would be well aware of the causes of erroneous behaviour in their products

Register to Reply Score 1 for Good Answer
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#3

Re: High No-Load Current on Transformers

03/15/2016 12:26 PM

Look at http:/en.wikipedia.org/wiki/Transformer

It actually discusses No Load losses with some detail.

Variations in how the cores are constructed might explain away this concern.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply Score 1 for Good Answer
4
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: High No-Load Current on Transformers

03/15/2016 4:08 PM

No-load losses tend to be almost exclusively due to magnetizing current current, so the thing you should be looking at is how the cores for the high loss transformers differ from the normal loss ones.

You have to examine things that affect the magnetic path; i.e., the type of steel, the flux density, how the laminations are formed, trimmed, insulated, stacked, etc., how the core is shaped, clamped, bonded, grounded, etc., the positioning of the windings, the leads/interconnections, the type of fasteners, their positioning/insulation, are there any unintended magnetic paths/short circuits, hidden eddy current paths, even the material of the tank, the positioning of the phase leads/bushings, etc., etc.

Also remember that any losses manifest themselves as heat/hot spots, so you may find that untanking a unit and and doing a thermal scan may help pinpoint where the excess losses are occurring.

All this presupposes that you have done all the necessary steps to ensure that the transformer design and construction is correct.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 4)
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#5
In reply to #4

Re: High No-Load Current on Transformers

03/16/2016 11:24 AM

I believe RAMConsult is on the correct pathway to explaining your issue with your transformers. I was going to say something that equates to a parallel capacitance to the primary or secondary, but other aspects of field saturation may have more to do with this, in terms of parasitic eddy currents.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

IdeaSmith (1); James Stewart (1); NotUrOrdinaryJoe (1); RAMConsult (1); spades (1)

Previous in Forum: Generator   Next in Forum: 11kV Line Insulator Sparking

Advertisement