Anonymous Poster #1

Calculation of FAD

04/01/2016 6:07 AM

first you have to find FAD for individual outlets and add all of them together, then you will total capacity of your compressor(FAD)

here,

we have formula,

Q(FAD)=[QN×(Ti+273)×1.013]/(273×Pi), unit L/s

where,

QN=flow of air from respective outlet, unit should be in L/s,

if some time the unite is in Nm3/min,

so u have to convert it,

which is, 16.667NL/s

Pi=pressure at ambient temperature=1 bar

Ti=ambient temperature.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: calculation of FAD

04/01/2016 6:57 AM

And...?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Calculation of FAD

04/01/2016 11:35 AM

You left a step out:

Q(FAD)=[QN×(Ti+273)×1.013]/[Then a Miracle Happens)(273×Pi), unit L/s

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Calculation of FAD

04/01/2016 12:08 PM

FAD = frequently added dimensions

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: Calculation of FAD

04/01/2016 4:01 PM

Cooling BTUs = CFM x ∆h x 4.5

• CFM = The fan CFM plotted on the fan tables, or measured at several points in the system

• ∆h = the enthalpy change through the system (we get this number by converting wet bulb readings.)

• 4.5 = the cooling BTU multiplier at sea level, or .075-lbs. of air per CFM x 60 (minutes in an hour.) This factor will also change at higher altitudes. BTU multipliers will also change due to extreme air temperatures.

http://contractingbusiness.com/archive/system-delivered-btu-calculation-basics

http://www.uigi.com/WebPsycH.html

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#5

Re: Calculation of FAD

04/02/2016 4:28 AM

The square brackets [] are superfluous

__________________
Give masochists a fair crack of the whip
Reply
Power-User

Join Date: Nov 2015
Posts: 335
#6

Re: Calculation of FAD

04/03/2016 11:26 AM

AP?

__________________
"And ye shall seek me, and find me, when ye shall search for me with all your heart."
Reply
Reply to Forum Thread 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Codemaster (1); JohnDG (1); lyn (1); Mr. small (1); SolarEagle (2)

Previous in Forum: Frozen Suction and Compressor   Next in Forum: IKEA Recalls Defective Allen/Hex Keys

Advertisement