17 comments
Rate Comments: Nested
Participant

Join Date: Mar 2016
Posts: 2

Frozen Suction and Compressor

03/31/2016 10:35 PM

Hi!

I have a water-water geothermic heat pump working with R407c where both evaporator and condenser are plated water permutors.

The issue is that all suction line including expansion valve, evaporator and even the bottom of the (hermetic) compressor are completely frozen. It starts to freeze like after 5 min of the compressor starts running...

What can be happening here?

It is an isolated machine with factory fluid charge. Filter has been changed recently and liquid visor indicates no humidity in the system.

Thanks a lot for your help

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#1

Re: Frozen suction and compressor

03/31/2016 11:05 PM

How is the flow across the evaporator?

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Frozen suction and compressor

04/01/2016 2:08 AM

I would check all the usual things....and fix the problem....If you can't do that, then call somebody who can.....We can't troubleshoot the system from here...well maybe we could if you would supply all the necessary information and readings, but I sense that's not likely...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Commentator

Join Date: Mar 2016
Posts: 86
#3

Re: Frozen suction and compressor

04/01/2016 2:42 AM

Start with the TEX - dump it.

Is it short-cycling?

__________________
Did Indecent Exposure create the need for darkroom ?
Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#4

Re: Frozen suction and compressor

04/01/2016 6:26 AM

What is a permutor?

__________________
Per Ardua Ad Astra
Register to Reply
Participant

Join Date: Mar 2016
Posts: 2
#6
In reply to #4

Re: Frozen suction and compressor

04/01/2016 8:21 AM

Sorry, I'm not a native English speaker and the word didn't came to my mind at that moment, it is an heat exchanger (fluid-to-water).

I'll be at the site again tomorrow so I will be able to provide any details you may see necessary. I'll make sure to provide evaporation and condensing temperatures, subcooling and superheating values and pressures before and after evaporator.

Any other information you think may be useful just ask and I'll try to provide it tomorrow.

By TEX means thermic expansion valve?

Many thanks in advance for your time and effort.

Register to Reply
Commentator

Join Date: Mar 2016
Posts: 86
#7
In reply to #6

Re: Frozen suction and compressor

04/01/2016 8:39 AM

Yes, TEX = Thermostatic Expansion Valve.

__________________
Did Indecent Exposure create the need for darkroom ?
Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#8
In reply to #6

Re: Frozen suction and compressor

04/01/2016 10:40 AM

If it is winter where you are and you are extracting heat from geothermal water to heat the home/factory, 3 possibilities come to mind.

1. Inadequate depth in the earth for the source water to be at deep earth equilibrium.

2. Low snow cover so the shallow source water is ready to freeze as soon as you extract a little heat.

3. Inadequate velocity of water circulation pump so water stays by the fins too long and freezes fast.

CURE

Deeper GTW source

Foam insulation for winter over the bed.

Higher pump velocity or volume capacity, perhaps right on the fins with a spreader

__________________
Per Ardua Ad Astra
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#9
In reply to #6

Re: Frozen suction and compressor

04/01/2016 12:20 PM

You could start with stated requirements by the manufacturer for the system to function properly...and take readings on what you have in actual location...If you are trying to operate the system outside the necessary requirements, then there will be a modification needed....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Frozen suction and compressor

04/01/2016 8:06 AM

Please describe the outcome of the telephone discussions that have taken place with the equipment manufacturer on this topic.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#10

Re: Frozen Suction and Compressor

04/01/2016 12:23 PM

Make certain the system is correctly charged with R407c, by consultation with the Original Equipment Manufacturer, and get back with us, and let us know if you survived the cold.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#11

Re: Frozen Suction and Compressor

04/01/2016 4:05 PM

Sounds like the water is not circulating....check pump and refrigerant pressures at start up after complete thaw....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#12

Re: Frozen Suction and Compressor

04/02/2016 5:16 AM

Exactly what is freezing?Is it the circulating water system,or the Freon system?

From what I can determine from the information given,it is the Freon side of the system that is freezing,on the suction side only?

Is it freezing only on the outside of the piping,or internally as well?

Are you using the heating mode or the cooling mode?

It is normal for the suction side to be cool,even sweating,in high humidity environment,but the pressure side should be hot,if all systems are doing their job.

The TXV is on the pressure side, after the condenser,so there should only be liquid Freon there for the TXV to regulate.

If there is not quite enough pressure on the Freon side,the evaporator will run very cold, due to the reduced pressure,and consequently, the temperature, of the Freon.

That would be my first guess at the problem with the limited information provided.

If the evaporator is partially clogged,you will be sending liquid Freon to the suction side of the compressor,which you will be able to hear as a rattling sound,but it will eventually destroy the compressor valves,unless it is a scroll type compressor.

Not much heat will be picked up by the Freon,and the suction side will not be very cold.

Check your system pressures, on both hi and lo sides,as well as the Super heat and Sub cooling temperatures and measure the in/out temperatures of the water on both sides of the evaporator and condenser.

This,combined with basic HVAC principles will reveal the problem.

Good luck!

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Member

Join Date: Mar 2016
Posts: 6
#13

Re: Frozen Suction and Compressor

04/02/2016 1:10 PM

If by frozen you mean ice has formed on these components, it tells me the saturaged evaporator temperature is at of below 32 deg F, and the dew point of the air surrounding these components is at or above 32 deg F. What's happening on the outside of the equipment should not affect it's performance if it's designed to operated unders such conditions.

Register to Reply
Power-User
Engineering Fields - Petroleum Engineering - Rig Electrician United States - Member - the Oil Patch Engineering Fields - Power Engineering - Drives & Gen's Engineering Fields - Instrumentation Engineering - Drive Control Popular Science - Cosmology -

Join Date: Jan 2010
Location: Houston off/on-shore @ Oil Patch
Posts: 223
Good Answers: 2
#14

Re: Frozen Suction and Compressor

04/02/2016 3:09 PM

If it's not no flow across the evaporator [slow flow, dirty heat exchanger tubes, wouldn't freeze it up that fast] you are low on R407c, if it's not new the leak will drop the level and it won't work at all and pump air into the system when you check it again.

__________________
Why do they make manhole covers round? so they won't fall in [before asking "Who is John Galt?"]
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#15

Re: Frozen Suction and Compressor

04/02/2016 3:12 PM

Sounds like the evaporator fan is not working....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#16

Re: Frozen Suction and Compressor

04/04/2016 1:44 AM

Check the Suction and discharge pressure and compare it with the O& M manual. Refrigerant is mixture and check for temperature glide aspect. Check leak for refrigerant and the operation of heat exchanger fans.

Register to Reply
Commentator

Join Date: Dec 2010
Posts: 80
Good Answers: 6
#17

Re: Frozen Suction and Compressor

04/04/2016 2:51 PM

Hello. I am late on this post. You may have already found your solution.

However i see English is not your native tongue.

Engineer speak can be very difficult for those where English is not their mother tongue.

I will probably catch some hell for this, but let me try some Plain English.

Frost on the low pressure side of an AC unit is common. It depends on the surrounding ambient air temperature and humidity etc.

However your description can also indicate too low of a pressure on the low side.

As explained in other posts, to diagnose the problem, a pressure reading is where to start.

If the pressure on the low side is too low, then you will want to check the high side pressure .

If both sides are low, the initial charge of refrigerant was not sufficient or has leaked off.

If the low side is low and the high side high, you most likely have a stuck expansion valve or a plugged filter / screen.

Either way , "if" your compressor's lubricating oil circulates with the refrigerant the compressor is being starved of lubricating oil and may be damaged.

If the system must be opened to repair, i suggest you pay close attention to any material caught by the filter. That can explain if the compressor is damaged or not.

If compressor material is found circulating in the system, all system parts have to be flushed / cleaned or replaced to prevent repeat failures.

Hope this helps.