GFCI for Welding Machines

04/03/2016 1:00 AM

Dear all,

I've been searching a lot about GFCI requirement for large welding machines( EGW and SAW, SMAW etc.).

The generator is connected to the panel ( 380 V p-p, 60 Hz). To make the connections easy, we installed outlets on the panel board itself (around 10 outlets each one above 63 amps). There isn't any single phase connection.

Please let me know whether GFCI is required? Would appreciate if you could provide me with NEC reference.

Thank you!

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: GFCI for Welding Machines

04/03/2016 2:20 AM

This is a pretty sketchy area...I would say that you should have a comprehensive grounding strategy in place that will stand up under scrutiny...If you don't have GFCI protection, then you better be able to show why it's not necessary, that your workers are protected as much as can be reasonably expected in this situation...and that some authority(OSHA) has signed off on it....

"In industrial establishments where conditions of maintenance and supervision ensure that only qualified personnel are involved, an assured equipment grounding conductor program as specified in 527.6(B)(2) is permitted for only those receptacle outlets used to supply equipment that would create a greater hazard if power was interrupted or those that have a design that is not compatible with GFCI protection."

http://ecmweb.com/code-basics/nec-requirements-ground-fault-circuit-interrupters-gfci

https://www.osha.gov/pls/oshaweb/owadisp.show_document?p_table=STANDARDS&p_id=9881

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: GFCI for Welding Machines

04/03/2016 3:33 AM

If you don't know the answer to this question, you should not be in a position to make the decision!

Certainly, asking an anonymous forum to give you advice on life critical circuit protection is reckless and irresponsible.

YES GFCI IS REQUIRED.

Register to Reply
Associate

Join Date: Jan 2015
Posts: 46
#3
In reply to #2

Re: GFCI for Welding Machines

04/03/2016 3:43 AM

okay... we've been asked by our safety manager to install GFCI on the panel board... to me it didn't make any sense as the welding plants are installed on a separate stand... all the welder has to work on are -ve and +ve terminals coming out of the machine... why would the gfci be required in this case.. i want to understand...

Register to Reply
2
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#6
In reply to #3

Re: GFCI for Welding Machines

04/03/2016 5:39 AM

The GFCI, as the name suggests, is there to protect against dangerous ground fault currents.

This has to everything do with a fault developing in the primary side of the welding circuit and nothing to do with the secondary, assuming that it is not an autotransformer welder.

If a fault to exposed metal should occur on the feed to, or within the machine itself, then the GFCI can be expected to isolate the circuit before someone gets seriously hurt.

A GFCI senses an imbalance in the currents flowing out through the device as compared to those returning through it, if they are not equal, then the device determines that some of that current is going elsewhere, possibly through a hapless worker, and it isolates the supply, hopefully before any damage is done.

It will not protect a person if they get between live conductors on either the primary or secondary sides of the welder.

Obviously, for your GFCI to function correctly, there must be an earth return path to the generator output. This would entail a ground connection to the star point, a corner delta, or other method of achieving the ground reference.

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: GFCI for Welding Machines

04/03/2016 4:41 AM

Just do as your manager has told you to do, you clearly aren't the one to make such decisions.

The GFCI isn't to protect the LV + - O/P it protects the incoming to the set, in doing so protecting the operator against any leakage between the windings or to the casing.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: GFCI for Welding Machines

04/03/2016 5:04 AM

Having read this and other threads you have started I think you should find a new occupation or stick to welding.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7

Re: GFCI for Welding Machines

04/03/2016 12:54 PM

Interestingly NFPA 70 (aka NEC) Article 630 "Electrical Welders" is silent on the matter, with Section 630.1 Scope referring only to "...(welding) apparatus...that is connected to an electrical supply system..." Typically this is interpreted as "look back to the supply side and its requirements" (my words, fwiw), so you'll have go back to the appropriate sections that deal with everything from your generator installation up/down to, and including, the welding receptacle(s).

Hire a qualified electrical contractor/engineer and let him deal with the AHJ (Authority Having Jurisdiction), then abide by their decisions (in writing); otherwise you'll be liable for any lawsuits that result from any electrical incident/accident from the entire installation.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: GFCI for Welding Machines

04/03/2016 1:03 PM

ACTUALLY, taking a strictly literal interpretation, a GFCI is a very SPECIFIC device that is ONLY required on 15 & 20A single phase residential circuits into which devices can be plugged into receptacles in wet areas, or outdoor receptacles. It is SPECIFICALLY limited to a maximum of 6mA of ground current, designed to trip at around 4mA. You basically cannot plug a 380V welder into one, so the entire question is moot.

I would also further speculate that anything rated for 380V is not designed to be used anywhere in the USA, so referencing the U.S. NEC also becomes moot.

Now IF, once again having to INTERPRET what you MIGHT be attempting, is that you are in the U.S. and for some strange reason are compelled to try to connect s 380V welder here, so you have bought a custom transformer to feed it, AND you have investigated and discovered that it will indeed work on 60Hz because if designed for 380V it is likely designed for 50Hz, then MAYBE you are asking if you must provide Ground Fault Potection, aka GFP then the answer would be, no. You are not compelled to provide GFP unless the service feed to it requires 1000A or more. You can, at your discretion, add it if you like.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#10
In reply to #8

Re: GFCI for Welding Machines

04/03/2016 5:33 PM

In N.S.W Australia - where I reside - it became law in 2011 for all socket outlets rated at 20 amps or less in workplaces to be RCD protected. This replaced the previous residential only requirement. This covers many smaller 3 phase welders, but wouldn't apply to the OPs ones.

All existing workplaces had 12 months to begin implementation, and 4 years to fully comply with the rule.

My understanding is that NEC rules were expanded in 2002 to include a number of non residential activities - ie. 547.5G agricultural buildings, 511.12 commercial garages, 555.19 marinas and boatyards, etc.

I had 30mA RCDs (minimum trip 15mA) installed for all outlets, both single and three phase, at my last workplace back in the nineties, 3 phase welders were regularly used from these outlets with no ill effects.

3 phase RCDs are available here up to 100 amps off the shelf and greater by order with trips ranging from 10mA to 300mA.

Register to Reply
Associate

Join Date: Jan 2015
Posts: 46
#11
In reply to #8

Re: GFCI for Welding Machines

04/03/2016 11:50 PM

Thank you. That does clarify.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#14
In reply to #8

Re: GFCI for Welding Machines

04/04/2016 5:56 AM

380/220V would indicate one of the Benelux countries so the NEC wouldn't apply. It's one of the few areas I don't have the codes/regulations for.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#9

Re: GFCI for Welding Machines

04/03/2016 5:25 PM

From y hands on experience GFI on anything but an outlet near a kitchen sink or bathroom is nothing but a nuisance and waste of good company time and money.

My experience is that a GFI on any portable generator/power station system is nothing but trouble. The primary problem being it's rare that any portable generator ever gets properly and sufficiently (If at all) earth grounded which makes the local generator frame ground nothing more than a floating ground and thus nearly useless.

Granted many will have their common line tied to their frame ground which then makes the unit safer for line to grounded objects but it also makes the GFI totally useless being it now has what is essentially a floating tap going someplace that is not of equal potential/ current path flow with the line side.

Now to make things worse welding power supplies often have some degree of internal connection between their lower voltage high current outputs and the frame grounds via capacitive coupling and or resistive coupling to bleed off any potential static charges that could be held or induced in the objects being welded on. That again makes for an odd combination of possible stray current flows that can mess with a GFI units ability to distinguish between a true earth fault and a false one.

So given that if you want to put GFI on a nonstandard multiphase portable generator powered welding system you might as well hire one guy to stand by the GFI and hit reset every few seconds after someone strikes a weld because you won't get a damn thing done other wise.

In the right applications and contexts of use a GFI is a very good thing. In the wrong ones where they serve no real gainful purpose they are just a waste of time and money and a source of a lot of frustrations and by my experience portable power systems and welding related work is not a place for them.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Jan 2015
Posts: 46
#12
In reply to #9

Re: GFCI for Welding Machines

04/04/2016 12:00 AM

Thanks for your detailed response.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13

Re: GFCI for Welding Machines

04/04/2016 5:43 AM

British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#15
In reply to #13

Re: GFCI for Welding Machines

04/04/2016 6:00 AM

BS7909

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Associate

Join Date: Aug 2015
Posts: 53
Good Answers: 2
#16

Re: GFCI for Welding Machines

04/04/2016 7:02 AM

I can't say if one is required. I can say that if you install the GFCI, you should be ready for a lot of unplanned shutdowns if it uses arc detection as a fault condition.

To a WELDER? Riiiiight!

Cortland Richmond

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#17
In reply to #16

Re: GFCI for Welding Machines

04/04/2016 11:45 AM

deleted

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Associate

Join Date: Jan 2015
Posts: 46
#18
In reply to #17

Re: GFCI for Welding Machines

04/05/2016 1:01 AM
Register to Reply
Register to Reply 18 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: