Troubleshooting Cathodic Protection Systems

08/01/2007 10:42 AM

We have been trying to located an intermittent short between a cathodically protected gas line and the copper grounding grid in a combustion turbine generating station.

The intermittent condition now has changed to a solid short dragging the pipe to soil potential down to -0.56V. We were operating at a -1.2 V on the best day as measured by a permanent reference cell hooked to our PI system. Manual pipe to soil potential readings verify the permanent cell output. The pipe is protected by a large anode bed with additional anodes installed at each point the pipe exits the ground.

The pipe has been dug up and exposed in a number of areas where pipe to soil potentials indicate the lowest potential ---with no shorts or grounds found.

In the general areas that point to the lower protection, we have installed double insulation (on both flanges on the valves where the piping comes from the ground).

Does anyone know of a technology that can locate a short within a few feet of the actual location?

My contact information is pcmyers@aep.com

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Trouble shooting cathodic protection system

08/02/2007 12:24 AM

Greetings,

An inexpensive ($5) radio (which does not have AGC auto gain control/volume regulation. Understand that the antenna of the radio when pointed vertical has a donut shaped best reception pattern around the antenna. On the tip of the antenna it has essentially no signal reception.

Arcing creates a lot of radio interference.

So take your radio into the area of interest with the antenna parallel to the ground, turn the volume up until you get noise, then move around the area, any time the noise increases use the tip of the antenna to isolate the spot and mark with a stake.

Using ultrasound may also find arcing, but the arcing can be so random that you will miss it with ultrasound.

Disconnecting the cathodic protection system and connecting a AC variac will create more arcing and may "burn" the area of interest in a continuous arc that is easier to find.

Dan

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#2
In reply to #1

Re: Trouble shooting cathodic protection system

08/02/2007 2:53 AM

WOW, absolutely brilliant. You have really done your homework on this subject....the radio tip is great, the other I will remember, but probably never use......

Many thanks.

__________________
"What others say about you reveals more about them, than it does you." Anon.