Alternator Exciter Field Polarity

04/09/2016 1:38 AM

Good morning,

I have lost the marking on exciter field wires F1 & F2 (+ -).

is there any way to check & confirm the polarity of exciter field winding ?

your early response will be highly appreciated.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Alternator exciter field Polarity

04/09/2016 1:59 AM

F1 is pos I think....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Alternator exciter field Polarity

04/09/2016 2:34 AM

Check the polarity of the flyback diode, if there is one. If not, then determine if there's any circuitry beyond the leads, if none then it doesn't really matter since swapping the field leads is equivalent to rotating the shaft 180º on a 2 pole machine.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#3

Re: Alternator exciter field Polarity

04/09/2016 10:15 AM

If it is self excited and the connections are reversed, it won't build up voltage on start up. The reason is that if the polarity is reversed, the residual magnetism will buck the applied field current causing it to reduce instead of build up.

http://newmachineparts.blogspot.com/2013/11/why-self-excited-shunt-generator-will.html

Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4
In reply to #3

Re: Alternator exciter field Polarity

04/09/2016 11:25 PM

Sorry, that's true for a self-excited shunt DC generator where the field brushes are directly connected across the output terminals; that's not the topology of an AC alternator.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#5
In reply to #4

Re: Alternator exciter field Polarity

04/10/2016 7:48 AM

Right, I was thinking of a DC exciter driving the alternator field.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6

Re: Alternator exciter field Polarity

04/10/2016 10:18 AM

I cannot see how it will make a difference, apologies if I am wrong.....but I simply don't understand the worry.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Nov 2015
Posts: 133
#7
In reply to #6

Re: Alternator exciter field Polarity

04/11/2016 12:02 AM

No forget it Andy, your response is late. OP is up to early response only. I'd like to add but, hell no.

__________________
formerly Legolaz
Register to Reply Score 1 for Off Topic
Anonymous Poster #1
#9
In reply to #7

Re: Alternator exciter field Polarity

04/11/2016 12:25 AM

...

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8
In reply to #6

Re: Alternator exciter field Polarity

04/11/2016 12:25 AM

If we assume, just for clarity a 3 phase stator, that is 3 fields and the rotor receives DC, variable value to handle variable loads, either via slip rings, or most probably via two cables sown the middle of the drive shaft, going to a single coil giving north and south magnetism.

If these exciter field connections are reversed, then the alternator output will be effectively "reversed" in comparison to its own output previously, but who the hell will ever notice that!!

It reverses every 1/50th of a second or 1/60 of a second either way, that is either 50 or 60 Hertz!! That the rotor shaft is simply turned 180° different to its previous orientation......

It will not make the slightest difference to anything else.......

Now if there were TWO alternators, built on the same shaft, that had to be "in sync" with each other, there would be a worry, but even then monitor the same phase on both using say a scope and see if the phasing is the same before connecting them to each other!!!

But how often are two alternators on the same shaft?????

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Participant

Join Date: Apr 2016
Posts: 4
#11
In reply to #8

Re: Alternator exciter field Polarity

04/11/2016 1:40 AM

Dear Andy,

Thanks for quick response, but still my question is not answer.

I would like to know if you have lost marking on exciter field F1,F2 (+ ,-)how to remark again, is there any way or procedure to check & confirm the polarity??

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#12
In reply to #11

Re: Alternator exciter field Polarity

04/11/2016 6:15 AM

Try reading my posts better, what I was saying is "IT DOES NOT MATTER ABOUT POLARITY!!"

Try it and see!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#10

Re: Alternator Exciter Field Polarity

04/11/2016 12:26 AM

How about an answer from you now?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#13

Re: Alternator Exciter Field Polarity

04/11/2016 9:01 AM

Use the residual magnetisation as an indication.

Run the machine un-loaded without excitation and isolated from any load.

Note the output voltage.

Add a small excitation current and see if the output voltage increases or decreases.

If it increases, you are in the original polarity. Mark it an test its validity with caution just in case this didn't work. (Nothing is 100% certain...)

While you are at it. Mark all the other field and phase terminals you may have in the plant at the next safe occasion to avoid this in the future...

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Register to Reply 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (4); Anonymous Poster (1); CM Patel (1); marcot (1); Peterpipper (1); RAMConsult (2); Rixter (2); SolarEagle (1)