Installation Of Armoured Cable On Trench

04/13/2016 12:26 PM

want to install a HT armored cable 95mm square in underground. The proposal is to install in a trench constructed with blocks and concrete. However, the same can be installed underground directly or in pipe and save cost. What are the disadvantages when the underground armored cable is not installed in a well constructed trench?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: INSTALLATION OF ARMOURED CABLE ON TRENCH

04/13/2016 12:51 PM

There are pros and cons to any method and you'll need an experienced engineer to decide the best route for your particular ambient/soil conditions. A properly constructed trench allows the cable to be laid in rather than pulled thereby limiting damage during installation, and easier detection and repair if there is a cable failure. However you need to evaluate the maximum ampacity given that the cable is not in direct contact with the surrounding soil, but this could be alleviated by placing thermal sand in the trench after the cables are installed.

Directly buried cables usually have the highest ampacity for a given size if the soil conditions are good, but are most likely to be damaged if the fill and cover materials are not carefully chosen, especially if there is rocky soil or a road with heavy equipment traffic directly over it. Properly constructed conduits help to protect against damage, but rely on good installation practice as the cables are pulled in.

Your best bet is to consult with someone familiar with the site conditions.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 3)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Installation Of Armoured Cable On Trench

04/13/2016 3:00 PM

Once the cable is installed a "sheath test" should be carried out before the trench is fully backfilled. Before the cable is terminated I test at 500V between the armourings and earth to show any damage to the serving that should be protecting the armourings.

It's easer to repair the sheath before problems appear years down the line.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#3

Re: Installation Of Armoured Cable On Trench

04/14/2016 3:29 AM

In answering your question, 'What are the disadvantages when the underground armored cable is not installed in a well constructed trench?"

The answer is: Nothing! The trench has nothing to do with the performance of the cable in transmitting voltage.

It does however have a correction factor on current rating that the cable may carry if the cable is installed in a trench, or duct or direct buried.

And your proposal of a trench is useless, unless one is provided the ground conditions, (geotech), the trench depth, width, run length, surface conditions, (between houses, mud huts, shops, open ground, rocks, dense jungle, open plains, soft soil etc).

Register to Reply Score 1 for Good Answer
Commentator

Join Date: May 2011
Posts: 73
Good Answers: 3
#4

Re: Installation Of Armoured Cable On Trench

04/14/2016 3:55 AM

In my limited experience, the most important reason for a properly constructed and surface indicated trench is that one day someone needs to dig in the area. The trench gives added protection and an indicator to work carefully.

We have just started planning phase 2 of our parts warehouse and I am sure the effort we put in during phase 1 to do a proper tranch will pay off.

Register to Reply
Power-User
United Kingdom - Member - Not quite retired Member

Join Date: Aug 2012
Location: Up an araucaria araucana tree, South London, United Kingdom
Posts: 132
Good Answers: 7
#5

Re: Installation Of Armoured Cable On Trench

04/14/2016 4:55 AM

The immediate disadvantage is that one could not lay more. There is a risk of accidental damage. Buried cables should have markers and/or indicating tape. Due to the dissipation of heat, directly buried cables have a slightly higher current carrying capacity - see the tables. A slightly smaller size of cable might be used, with further saving.

Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#6
In reply to #5

Re: Installation Of Armoured Cable On Trench

04/14/2016 5:12 AM

Reducing cable size will not promote a cost saving if the required load has been determined. Going bigger allows for further expansion, slightly higher costs for a cable and less trouble in upgrading a cable for future loads and a 10% margin of safety. However, the trend has always been to load cables to the max to optimise the cable life span and initial cost.

A trench, duct or direct buried has the same costs to construct, Only the cable price varies and makes an impact on costs. The back fill materials may vary slightly if CBS, or river sand is used as the thermal medium, but that is negligible compared to cable price.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7
In reply to #6

Re: Installation Of Armoured Cable On Trench

04/14/2016 10:35 PM

"...A trench, duct or direct buried has the same costs to construct,..." Really?

A 50HP DitchWitch can cut a 6" wide, 24" deep trench at about 10-12fpm in a single pass with a single operator (dependent on soil conditions of course). Compare that with creating a concrete encased trench or duct which you have to excavate, place forms, pour concrete, wait for it to harden, strip the forms, place the supports, etc.; time, materials, and labor requirements are at least 5 -10 times greater than direct burial.

That's one of the reasons why utilities would rather do overhead than underground where possible.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#8
In reply to #7

Re: Installation Of Armoured Cable On Trench

04/15/2016 6:02 AM

Indeed really. Read the entire statement. And I would assume, (which was wrong of me), that anyone knowing cable installations, that a BoM for a cable trench does not change anywhere in the world. Direct bury+X, ducted =X+1 and constructed=X+2. There is no cost saving to gain. But, on cable prices that fluctuates daily on a copper price this is the biggest cost of which very little control can be gained.

Given that the lad has provide zero detail if he has a road crossing, the type of medium to be excavated, if he has the reserve granted to install the cable below ground any other details I would not offer the in depth knowledge of costs of BoM for cable trenches, but would again assume that anyone doing excavations for cables would have an inkling on costs, again the costs of trenching all have the same universal costs and no cost savings.

OHL will be far cheaper if he was going a long distance, but as he has a cable in mind, OHL is of no value here. And OHL is a different ball game in costs.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#9
In reply to #8

Re: Installation Of Armoured Cable On Trench

04/15/2016 2:06 PM

You are correct, there are not enough details to assist the OP in going beyond his original question. But the argument that two men and a machine that can trench and fill 5-10ft per minute costs the same as a multi-person construction crew that takes a day to construct a 100 ft. lined trench is unfounded, unless of course the labor and materials have little or no cost.

The BOM for direct burial is simply the hourly rate for the laborer, operator, and the trencher divided by the length. The BOM for a three sided concrete trench includes a backhoe and its operator, two forms makers, the forms and concrete, labor for pouring and stripping, plus the cover/backfill material and labor. All that additional time, materials, and labor makes the cost per hundred feet at least an order of magnitude higher than direct burial, and this doesn't include the cable or its installation labor. btw- the cable is only 25-35% of the overall cost for anything other than direct burial.

Please use your copy of "RS Means Construction Cost Estimating Data" to prove me wrong.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

abotha (1); Geoffrey36 (1); IQ (3); RAMConsult (3); TonyS (1)

Previous in Forum: Earthing Current Limiting   Next in Forum: Detectors Above Ceiling

Advertisement