hi guys,
i have a task to calculate earthing resistance to connect with transformer,
what i have is;
transformer 3 MVA @ 13.8 Kv
limit earth fault current to 200 Amperes.
what i did to calculate is:
V(neutral to phase) = 13.8kv / sqrt(3) = 7.9 Kv
total current through transformer= 3MVA/(13.8kv X sqrt3)= 125 Amps
V= IR
for R,
R= V/I
R=7.9Kv/125=63.2 Ohms
R=63.2 Ohms
now, what i am confused is, if putting this value resistance, how do i justify that this 63 ohms will limit earth current upto 200 amps.
please guide. also if there is any mistake in my calculation please advise
"Almost" Good Answers: