Phase Shift Across Transformers

06/11/2016 2:24 AM

Hi,

It is normal to have a generator transformer with a vector group dYN. On our system these transformers are dYN1. All through the transmission network, there is no phase shift as transformers are YNyn0. The phase shift only happens again across distribution transformers which are Dyn11.

If I use a distribution transformer of Vector group Dyn1 on this network, without paralleling it with the existing Dyn11 transformer, would this have any impact on the customer(s)?

Thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Phase shift across transformers

06/11/2016 3:47 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Phase shift across transformers

06/11/2016 4:34 AM

So long as you don’t try to parallel them your customers won’t know the difference.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#3

Re: Phase Shift Across Transformers

06/12/2016 12:18 AM

A transformer connection . . . dYn just does not exist.

Register to Reply
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#4

Re: Phase Shift Across Transformers

06/13/2016 10:35 AM

The only customer issue would be if a fault condition occurs in the transformer at some future time. If the Dyn0 transformer fails for any reason, the customers will have an outage or at least a grid bump as the lines are switched to the other transformers. Depending on how fast the switching works, the customer will potentially see the 11 degree phase shift as the load shifts from the zero degree shifted source to the 11 degree shifted source. This is because the transformer is essentially stand alone.

Those customers on the paralleled transformers wouldn't see a major change as the load would transfer to the paralleled transformers.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5
In reply to #4

Re: Phase Shift Across Transformers

06/13/2016 11:09 AM

Ummm, the 11 doesn't stand for 11degrees, it represents the number of 30 degree shifts from zero going clockwise. In this case it means either 330 degrees or, as a power engineer would read it, -30 degrees, from the reference vector.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#6
In reply to #5

Re: Phase Shift Across Transformers

06/13/2016 12:25 PM

OK, so 11 "hours". Same issue.

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Jpfalt (2); olehwi (1); RAMConsult (1); SolarEagle (1); TonyS (1)

Previous in Forum: What Happens To The Photons Generated By Laser Cooling?   Next in Forum: Fan Regulator Using Arduino

Advertisement