PFC To Motors On VFD

06/14/2016 4:38 AM

Is PFC necessary to motors already in VFD or VFD already suffice efficient operation of motors?

__________________
"And ye shall seek me, and find me, when ye shall search for me with all your heart."
Register to Reply
Pathfinder Tags: VFD vs. PFC
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: PFC to motors on VFD

06/14/2016 6:52 AM

Assumptions:

  1. PFC=Power Factor Correction
  2. VFD=Variable Frequency Drive.

The purpose of PFC is to reduce the current flowing in the feeder cable for the same load and the losses associated with the higher current. It can be justified economically on the basis of some combination of avoiding the up-sizing of cables, or of avoiding a penalty tariff being imposed by the utility company, or other possibilities.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: PFC To Motors On VFD

06/14/2016 9:48 AM

"In general, power factor correction capacitors should not be used with AFDs."

http://www.ab.com/support/abdrives/documentation/techpapers/qanda01.htm

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: PFC To Motors On VFD

06/14/2016 12:23 PM

The VFD will inherently correct the displacement power factor seen by the system to .95 or better. So not only are they not needed, but they can/will cause more problems if not done right, which involves significant added cost and space (tuned reactors) with no significant additional benefit.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#4

Re: PFC To Motors On VFD

06/15/2016 6:35 AM

1) A motor needs reactive energy for building its magnetic field.

2) The input power from a VFD flows through a rectifier and the current in a diode rectifier is in line with the voltage over the diode rectifier. (seen in time, current and voltage flow of don’t flow at the same moment.) This means that a VFD can only take active power out of the supply grid.

3) Looking at point 1) and 2) I conclude that the reactive energy needed for the motor must come from the capacitors inside the VFD.

4) A motor with a low PF will need more reactive power to operate. So the total power (active + reactive) the flows from the VFD to the motor will be high. This power will flow through the IGBT’s and the switching losses in the IGBT’s will be higher.

5) Can I conclude that a combination VFD + motor with low PF is less efficient than the combination VFD + motor with higher PF ?

Register to Reply
Register to Reply 4 comments