I am facing one problem in vacuum column level measurement in VV-008 (Slop distillate POT) in CDU/VDU, where VV-008 pressure is -783 mmHg i.e. -10644.96 mmwc.
On 24.06.2016 we mounted a new remote diaphragm seal type transmitter replacing the earlier one, with new steam tracing, new glass wool insulation, both upper & lower LT tapings were de choked/cleaned.
I entered the following values as LRV(lower range value) and URV(upper range value).
LRV: -1620 mmwc
URV: -216 mmwc
C to C distance(upper and lower tapings distance)is 1530mm. Specific gravity of the liquid, Vacuum Residue: 0.9
At zero conditions i.e. both upper and lower root isolation valves closed, Diaphragm spacer rings drain and vent caps kept opened , then I found PV: -1620mmwc which I had entered as LRV.
For URV, -1620+ (1530x 0.9)= -216 mmwc.
As I have not considered the vacuum factor for above calculation so i have doubt on my LRV and URV values.
There is no LG in VV-008 for cross check, like other sections of vacuum column where we can cross check with the LG.
Level Transmitter service is vacuum column slop distillate, Vacuum column pressure -676mmHg. i.e. -9190mmWC.
Kindly enlighten me about how to calculate LRV and URV values in vacuum column level transmitter.