Running A Motor In Star Mode At 60% Load

07/12/2016 5:01 AM

we are having a deep pan conveyor with 37KW motor and it is fitted with Del star converter.The motor is always running at20-24 KW.In my opinion,we have to run the motor in star mode if motor is running with less than 50%.In this case,this is 18.5 KW.But motor is running with 20-24 Kw.Since it is fitted with del star converter,can I run the motor in star mode when the load is 20 to 24Kw.This will help me in using Del star converter and also I may get energy savings.Kindly clarify whether motor will run properly or will it fail.And also.what could be KVAh consumption in both modes.Full load of motor is 63Amps and it is running with 31 to 35 Amps.Please clarify.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: running a motor in star mode at 60% load

07/12/2016 5:11 AM

Give up on the prospect of energy savings on this motor by running in star. If energy savings are desired with no equipment changes, then just switch it off when it is not needed.

If equipment changes can be justified then it is better to down-size the motor for a replacement with a lower kW rating that is to be run in delta, and cascade-out the larger motor ether for redeployment elsewhere or for value recovery upon sale. Once the replacement motor is to hand and being installed, remember to re-set the motor overload device to a lower full load current setting so that the motor is properly protected.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Anonymous Poster #1
#7
In reply to #1

Re: running a motor in star mode at 60% load

07/14/2016 4:07 AM

ether either

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: running a motor in star mode at 60% load

07/12/2016 6:37 AM

There is no economic reason to change from ∆ to Y other than to line the pockets of unscrupulous merchants. The motor will draw the power it requires regardless the connection method.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Running A Motor In Star Mode At 60% Load

07/12/2016 11:22 AM

Once again, you are searching for free ways to save money that do not exist.

You should hire a competent electrician or at least TRY to understand what you are asking.

Analyzing Electric Power Quality in Arc Furnaces - Icrepq.com

Power Factor - Arc Furnace - Mike Holt's Forum

Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Running A Motor In Star Mode At 60% Load

07/12/2016 4:37 PM

And on top of all that, your math is wrong. In Star, the capacity of the motor is not reduced TO 60%, it is reduced BY 67%, to 33% of it's design rating. In Star, any load of more than 12kW will overload your motor and fry it.

And.... there is almost zero real energy savings. An AC motor only uses what the load demands of it, plus a little bit of losses in making the iron and copper into a motor. The load is the load, regardless of how you connect the motor. So the only POSSIBLE energy savings come from a slight decrease in a portion of the losses. Losses in an AC motor are divided into 4 parts, not equally. Most of the losses are I2t losses, so they are directly related to load / torque, meaning those losses are going to be the same regardless of your connection. A small portion is windage; same, and friction; same. The only thing you can save on is a percentage of the magnetic losses, which are related to the voltage applied. So in Star, the voltage across the coils is 58% of what it is in Delta, so those losses are reduced by 42%. But those losses only account for about 10% of the total losses, which on a motor is maybe 10-15% of the total energy. So running in Star might save you 42% of 10% of 15% at best. That is .04%. Not 4%, 0.04%! Not even worth the cost of doing it and running the risk of stalling.

Simple truth to remember for ALL schemes about saving energy:

You can ONLY save what is WASTED, not what is USEFUL.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#5

Re: Running A Motor In Star Mode At 60% Load

07/13/2016 6:22 AM

Go for VFD you will save lot of Power.

__________________
Subramanyam
Register to Reply Score 1 for Off Topic
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#6
In reply to #5

Re: Running A Motor In Star Mode At 60% Load

07/13/2016 12:22 PM

If you can slow it down...

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8
In reply to #5

Re: Running A Motor In Star Mode At 60% Load

07/14/2016 4:45 AM

You will not save energy on a conveyor by using a VFD. Again, no wasted energy. If you slow the conveyor, it does less work. Energy is power across time, but work is as well, so less work = more time, energy stays the same.

You can only save energy using VFDs on CENTRIFUGAL pumps and fans by REPLACING more wasteful means of flow control like throttling valves or vane controls.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); JRaef (2); kvsubramanyam (1); lyn (1); PWSlack (1); rwilliams (1); TonyS (1)

Previous in Forum: Using 16v 83F Super Capacitors 2ith Lead Acid Battery Bank   Next in Forum: Autotransformer Motor Controller For Submersible Pump

Advertisement