Hi.
This is to solicit your idea on our breakdown case for 69kV Surge Arrester.
We had a power transformer 230/69kV (Y-Y) with a feeder of about 20km. Before the customer we had a metering CT and PT protected by a surge arrester. There was an incident where the line auto-tripped then auto-reclosed. However, customer complained about low voltage. Upon inspection, in between our feeder (about 11km) a jumper loop was openned. Thus, the customer experienced unbalance voltage. The open loop was Phase C and this condition persist for almost 3 hours. Upon arrival of line personnel, the line was shutdown for correction. Then, after repair, the line was attempted to be energized. However, the arrester (Phase C) at our metering point breaks down (explode).
Isn't it the overvoltage will occur on the unfaulted phase. But, the busted arrester was the same phase as with the open phase feeder line. Is it possible that during the line-to-ground- fault the energy created by the fault surpassed the rating of the arrester? if not, what is the possible cause of arrester breakdwon?
Good Answers: