07/28/2016 6:54 AM
Hello guys, I am an electrical engineer working in a cement plant (7200 TPD), we are facing a serious issue of explosion in power factor correction panel since the plant was commissioned (2005). None of the capacitor explode but the circuit components like flashing in magnetic contactors, breaking of cables that connect capacitor bank to main bus bar and damaging of the circuit breaker at its terminals.
We are using
AEG Designed 50 KVAR per stage Power Factor Improvement Panel
Voltage: 400 Volt
Controller: AEG BELUK BLR MC 12 Power Factor Correction
Capacitor: AEG PAB DPM 5.05/446
Cable: 35 mm2 which connects capacitor bank to bus bar
(Normally set to 0.96i lagging)
Please suggest some modifications if you've faced the same problem.
Re: Explosion in Power Factor Correction Panel
07/28/2016 8:08 AM
Your best bet, Mildred, is to ring the original equipment manufacturer and arrange for a call-out. Seriously!
Good moaning!
Good Answers: 444
07/28/2016 9:44 AM
"...None of the capacitor explode..., that's because they are fitted with overpressure devices that also break the circuit. Cables break when there is a massive fault current somewhere, you need to determine the source of the fault and the damage to the PFC system. Follow Crabtree's advice and call the OEM, to do otherwise is folly.
Good Answers: 131
07/28/2016 3:36 PM
Since we cannot see the power factor correction panel from here, and don't know any of its history, some of the questions a qualified testing and repair contractor will ask would be: 1. What is the environment in which the panel is installed? Is there air filtering to prevent cement dust from entering the panel and contaminating the components? Is it in a location in which the temperature, humidity, and other environmental conditions are within its specifications? 2. What are the electrical conditions to which the panel is exposed? Is the electrical service (voltage, frequency, etc.) within specified limits? Were there any excursions of the electrical service outside of limits before the panel failed? 3. What routine maintenance and testing was done on the panel to assure that all its components were clean and operating properly? Were all connections properly tightened and insulated? Had anyone inspected the panel prior to the failure to determine if there were any conditions that need correction? 4. Were personnel properly trained in the operation and maintenance of the panel, and was it operated within its design specifications? Was the panel properly specified in the first place, with regard to the operating conditions and purpose? So many questions, so little information. If you answer these, you may come upon the answer you are looking for by yourself...
07/28/2016 3:49 PM
First, I'd replace the electrical engineer who doesn't know what to do!
Get one that can call in a competent repair technician and who is capable of learning how his equipment operates and how to troubleshoot and repair the equipment for which he is responsible.
07/29/2016 12:44 AM
If you don't know the answer remaining silent is the best option.
Register to Reply Off Topic (Score 10)
07/29/2016 5:07 PM
That would make CR4 completely superfluous!
07/29/2016 6:16 PM
If the unknowing remained silent, you would not have come here to ask a question to which you did not know the answer!
07/28/2016 9:25 PM
The recommended modification is to replace all damaged equipment to the point that it works again and also works in the future.
This would involve a root cause analyses of the event and determination of the controls to prevent it from happening again. All modifications should strife for perfectness and usability.
Good Answers: 117
07/29/2016 2:07 AM
Why don't you look at the last time PPM was done, who did it and what did they do!
The reasons for your problem are extensive, you have to start your own investigation and then expand your search for the problem.
It has already been posted that you call the manufacturer.... Good idea!
07/29/2016 4:30 AM
Please look at "When" in these events have happened. I would suppose that your system is good and functionalinsteady state situation andthat some transient is causing an electrical overload of the other components.
Something like a very big motor being disconnected while at full load. Induced back EMF causing high inrust current to capacitors (that appear as low impedance path) and overloading the weaker elements.
Some of your other comments indicate possible poor assembly/maintenance/repair processes. (You mention "breaking of cables" rather than fusing.)
VERY Looooong time since I was anywhere near that sort of gear.
07/29/2016 1:27 PM
Flashing visible in contactors may be normal, especially large air contactors are required to switch almost pure leading reactive current. If contactors are wearing out, then perhaps your controller has a problem, switching too often. Assumes this install has been running trouble free up until now.
The other problem with cables & contactors breaking are likely due to excessive heat. Since the assembly worked at one time, your connections are loose or contaminated at the bus bars. Wire doesn't normally break until the insulation has been crisped off due to heat.
After years of switching, I wouldn't be surprised if the contacts on the contactors were burned away to nothing, leaving some open circuits or poor arc extinguishing capability, and perhaps high resistance connections creating heat to be conducted to the terminals.
Careful use of a clamp on ammeter can give you some clues as to which capacitors are still working, and how the current compares to the wire & ambient temperature rating. Your 35mm wire is adequate for each step.
7
Good Answers: 804
07/29/2016 7:57 PM
Preface: I absolutely HATE Power Factor Control done this way. It NEVER ends well in my opinion, the best you can hope for is that the expected catastrophic failure happens after you retire...
I agree on the issue of the contactors. Switching of capacitors is a special kind of duty, you need contactors rated for the task. In addition, these contactors must have a "dampening resistor" across each pole to prevent the inrush of capacitor charging current causing damage to everything in the circuit. The dampening resistors are controlled by separate parallel contacts interlocked with the main contacts in such a way as to allow the resistor to be in series just BEFORE the main contacts close, then shunted or opened when the main contacts close (because they are only needed for a few cycles).
This is what those special contactors and the circuits should look like:
The extra block on the top that has the coiled wires on it contains the dampening resistors and the early-make contacts. The wires are coiled because that inrush current will attempt to flow AT THE AVAILABLE FAULT CURRENT LEVEL for those few cycles, which makes the wires "dance" from magnetic forces. The coils act like shock absorbers so that they don't pull out of the terminals. Your system may or may not have the exact same physical arrangement, but the dampening resistors SHOULD be in the circuit somewhere.
Something that happens all too often is that the resistors eventually fail, and they fail open. Once they are not there, the rest of the components get all of the stresses associated with the extremely high inrush current of the capacitors. So the contacts of the contactors burn more, the main power leads start to "dance" and stress their terminations, and eventually, the capacitors themselves can swell and fail.
One thing that can cause the resistors to fail is that the system design itself is inappropriately selected, or something has changed. What that means is that the PF changes so dynamically that the controller is stepping caps in and out very rapidly; more rapidly than it should. the contactors are not supposed to be allowed to close until the caps have bled down to less than 50V, and that takes time. The controller usually has minimum time between step settings, but someone may have changed the setting because they (incorrectly) though that it was not tracking the power factor closely enough. That is actually the result of someone not understanding how it works and what the ramifications might be of making those changes.
You have your work cut out for you...
Good Answers: 70
07/29/2016 10:53 PM
Well stated & a GA from me
08/04/2016 3:41 AM
Capacitors may also fail due presence of excessive line harmonics since capacitors act as sink for harmonics, thereby may enhance operating temperature , excessive voltage, etc. Therefore you may check presence of line harmonics by connecting Power Quality Analyser.
Manindra
Manindra