AFE/ISU In Drives - Regenerative Breaking.

08/16/2016 1:05 AM

AFE - Active Front End Or ISU-IGBT Supply Unit is used In multi drive units where Common DC Supply is fed to Individual inverter drives.

AFE/ISU is a combination of AC Filter and Converter units to feed DC Supply.

During Regenerative breaking AFE/ISU Converter acts as Inverter and feed supply back to Source. Now my Questions are

1) How converter act as inverter during regenerative breaking ? means how single unit can work as converter and inverter both. reply plz in details or suggest for any reading materials.

2) AFE/ISU saves energy by feed supply back to source. is there any calculation to calculate how much energy can be saved ?

We have 1020 KVA (2*510KVA) ISU Units used in Cranes. 510KVA -200t- Main Hoist Motor Drive. 210KVA - 40t-Aux.Hoist Multi Module Drive, 150KVA For LT and 105 KVA For CT.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: AFE/ISU In Drives - Regenerative Breaking.

08/16/2016 8:34 AM

1) instead of a passive rectifier to convert from AC to DC, the front end is "active" in that it is another inverter. So to convert, the transistors are fired in a pattern that rectifies. In regeneration, it changes the pattern to being an inverter, measures and synchs up to the line so that motor kinetic energy that becomes excess energy on the DC bus gets pumped back into the source.

The cost of this is that the AFE drive will cost you accordingly, in that you are essentially buying two drives for one motor. The inverter is the more expensive part of a drive compared to a passive rectifier, plus an AFE requires extra filtering, line sensing for synchronizing and protections to avoid killing line workers by regenerating into downed power lines all those extras add up to the AFE being twice as expensive

2) there is no real "energy savings", because savings can only come from the elimination of waste. There is some energy recovery, which is a little different. The energy you recover is the exact same energy you used to accelerate the load in the first place, minus the losses inside of the drive. Marketing people like to call this energy savings, but if you cannot realize it without turning off the drive, what energy have you saved? As an example, if you start and stop a machine 20 times per hour using braking, you can realize significant savings in cost of energy by recovering some of the accelerating energy when braking. This is the real value of this technology. But if you accelerate once, then never shut down for 6 months, or of your load down not require braking and can coast to a stop every time you use it, you realize almost no return on the investment in the extra cost of the AFE drive. The recovered cost of acceleration energy for an occasional stop doesn't add up to enough energy cost recovery to justify the expense to make it happen. You must thoroughly investigate the entire process.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Member

Join Date: Oct 2010
Posts: 9
#3
In reply to #1

Re: AFE/ISU In Drives - Regenerative Breaking.

08/16/2016 1:31 PM

Thans a lot Mr. JRaef.

In My case we are using ABB ISU for common DC Bus supply for all Inverters.

In each ISU - 1 Filter unit and 2 Converter Modules are installed. (510KVA*2).

1) We have more than 20 On/Off operations of 200T Main Hoist ( 510KVA) and 40T Auxiliary Hoist (250KVA) in One Hour. ISU Remains 'ON' continue.

In that case what will be energy savings ? we forget about monetary savings. but i want to know that how much energy is pumped back into the source. and one more thing that, on what calculation base, ISU capacity is designed ?

Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4
In reply to #3

Re: AFE/ISU In Drives - Regenerative Breaking.

08/16/2016 3:57 PM

Energy SAVINGS = Zero in my opinion, because no energy is really being wasted here, so you don't have an opportunity to eliminate waste.

Energy RECOVERY = variable but only when lowering a load. Energy recovery while lowering is slightly less power than the energy consumed in lifting, likely around 90%, because now you have switching losses on both ends of the drive, not just the back end, plus the losses in the extra filtering necessary. But remember, POWER is not ENERGY, energy is power x time. So when lowering a load on a hoist, you are not going to be regenerating for the entire lowering operation time AND the power you can recover has everything to do with the potential kinetic energy of the load.

For example first lets look at a hypothetical "Sisyphean" situation situation where you lift a load, then lower the exact same load (for some unknown reason). When lifting, if it takes 400kW for 1 minute, that is 6.67kWH. When lowering, most of the time it is going to to coast, but when you want to STOP it at the desired level, it might brake for 5 seconds at the end of travel. Therefore when lowering, it regenerates 380kW for 5 seconds (.00028Hr), so the recovered energy is 1.05 kWH. The percentage of energy you have RECOVERED then is then 1.05/6.67 = 15.8% of that operation. But I doubt that is what will really take place. If you are for example lifting containers onto a ship, you recover almost NOTHING, because you have EXPENDED the energy to lift it, then the ship sails away with it and the potential energy represented by the weight of the container contents. You therefore DO NOT get the benefit of recovering even that small amount of energy. All you are going to be doing is lowering the CRANE ITSELF again, and MAYBE an empty container. So you might recover 90% of whatever potential kinetic energy exists in an empty container (the weight of the crane itself is constant either way). So if it took only 100kW to lift an EMPTY container, you can recover 90% of that for the braking time, .00028Hr x 90kW = 0.25kW, which is .3% energy recovery.

Do you see what I am getting at here? There is no simplistic way to quantify the energy recovery potential, far too many variables. But in my opinion, it's not the REASON you should use AFE drives. The reason is that regen braking is best for highly repetitive operations because it puts less strain on components of the system, which increases reliability.

Capacity is whatever the mfr states it is. If it is a 400kW drive, it can move 400kW in either direction safely.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: AFE/ISU In Drives - Regenerative Breaking.

08/16/2016 10:14 AM

I should have added however that for cranes, it makes good economic sense for the hoists, because you will alwayse need braking, but maybe not for the travel. Since you say these are hoists, they are likely the right application for AFE regen drives.

The alternative is to use dynamic braking with brake resistors, but for applications where there is a lot of braking involved, there is a risk of resistor burn-out, so coupled with the small amount of energy recovery, AFE drives win.

By the way, NEVER remove or otherwise eliminate MECHANICAL brakes for hoists, because if power fails, electrical braking is gone. But by using the electrical braking first, then using the mechanical brakes as "parking brakes" only, they essentially never wear out. This however requires that the VFD have a feature called (by many), "torque proving" that means the drive will put the motor into providing 100% torque while still at zero speed with the mechanical brake deployed. Then when you want to raise or lower the hoist, it only releases the mechanical brake after it knows for sure that the motor can hold it. Without that, if the load BEGINS to drop, it takes many multiples of the amount of holding torque to stop it. That means your motor would need to be extremely over sized.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Guru

Join Date: Jul 2016
Posts: 1369
Good Answers: 105
#8
In reply to #2

Re: AFE/ISU In Drives - Regenerative Breaking.

08/17/2016 8:44 PM

The heat dissipated by dynamic braking resistors is your energy not recovered. The sizing programs for dynamic braking resistors could help you estimate the recovery rate of your power converter, giving you inputs for time & load, duty cycle.

For a detailed look, see this. On-line calculators are simplified, but might meet your needs for accuracy.

http://literature.rockwellautomation.com/idc/groups/literature/documents/at/pflex-at001_-en-p.pdf

You can estimate the savings of an active front end (converter) using the efficiency ratings of the equipment, which the manufacturer should be able to give you quite accurately. You can consider the published heat gain of the converter equipment as offsetting some of the heat savings when compared with resistors.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: AFE/ISU In Drives - Regenerative Breaking.

08/16/2016 3:58 PM

Bonus points for me, that's likely the first time in over 40 years I have had the chance to use the word "sisyphean" in a sentence!

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#6

Re: AFE/ISU In Drives - Regenerative Breaking.

08/16/2016 4:34 PM

A driven DC motor is called a generator. Are you sure the actual power at the wheels is not DC? If it is AC, then I suppose the motors may also be alternators when driven (don't ask me how). The inverters would have to have some sort of back-feed accepting network to rectify the resulting excess AC power present at the output leads of the inverter back to DC for "storage". Doesn't there have to be a phase sensing component to gate this power back to diodes?

(1) how is breaking regenerative? Seems irreversible and destructive to me. Did you mean braking?

(2) to calculate the magnitude of regenerative energy one has to have all the physics present, including mass, velocity, frictional losses, electrical inefficiency of pushing electrons back to the source, etc.

(3) the crane mass rating does not necessarily reveal the physics of the unit in motion.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1369
Good Answers: 105
#7

Re: AFE/ISU In Drives - Regenerative Breaking.

08/17/2016 2:21 PM

Question 1) 3 phase SCR Power Converter, a set of thyristors 6 pulse (Fwd & Rev) set up for regeneration as well as motoring (a repurposed DC Drive, in essence) can charge & discharge the dc bus used for the inverters.

Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

cmaguna (1); James Stewart (1); JRaef (4); rwilliams (2)

Previous in Forum: How Do You Convert a Synchronous Generator Inertia From 1.0 tm2 to s?   Next in Forum: Efficiency Calculation For A VFD Drive

Advertisement