11KV Gensets Neutral Connection

08/18/2016 8:41 AM

Hi.

I have 8nos 11Kv DG sets are there which are running in parallel,Kindly suggest Whether i need to go for individual NGR for each DG's or one can be sufficient for all the Dg's.Kindly explain.

Regards

Murali

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: 11KV Gensets Neutral Connection

08/18/2016 10:48 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#2

Re: 11KV Gensets Neutral Connection

08/18/2016 1:32 PM

Looking back at your previous questions posted I'm surprised you haven't burnt the place down yet or killed yourself.

Does your boss know your lack of electrical skills? Or that your electrical knowledge is dependant on CR4® answers to your questions?

You are a different candidate for the Darwin's Awards. Hopefully you won't take someone with you.

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply Score 2 for Off Topic
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#3

Re: 11KV Gensets Neutral Connection

08/19/2016 3:56 AM

I have seen a project where 5 DG sets (6MW each) have their neutrals bussed and connected to a single NGR. However, each Generator neutral had its own isolator (located before bus formation).

__________________
Raghunath
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#4

Re: 11KV Gensets Neutral Connection

08/20/2016 3:06 PM

Ask yourself if you want a load of current circulation in those neutrals first.

__________________
Good moaning!
Register to Reply
Register to Reply 4 comments