Anonymous Poster #1

Differential Relay Tripping

08/25/2016 6:29 AM

The differential relay does not trip on transformer energization but trips when a HT motor is started. What could be the possible reason for this? the CT wiring and the settings seems to be okay.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#1

Re: Differential Relay Tripping

08/25/2016 8:26 AM

Looks like the transformer could be alright while the HT motor isnt, but then the information is so scarce I would call this a wild guess!

__________________
Common Sense Dictates
Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Differential Relay Tripping

08/25/2016 9:12 AM

"...seems to be okay...", if it were the differential wouldn't be tripping. Your job is to change "seems" to "is verified", until then no one can help you.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Differential Relay Tripping

08/25/2016 9:48 AM

What tests have been run on the CT and the Motor??

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4
In reply to #3

Re: Differential Relay Tripping

08/25/2016 11:30 AM

You seem to want to know the problem without troubleshooting the equipment...this is not possible...

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#5

Re: Differential Relay Tripping

08/25/2016 11:31 AM

Since we don't have a circuit diagram, it's impossible to give a good answer.

A differential relay trips (is energized) when two currents are not equal. It is commonly used in Ground Fault Interrupter (GFI) circuits.

Are we talking about a GFI circuit? If so, it indicates that there is a ground return path in the HT motor where current is returning to the supply through the ground and not through the neutral.

Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#6

Re: Differential Relay Tripping

08/25/2016 1:30 PM

This is just a shot in the dark, but someone left the discomboobulator engaged. That fed back to the HT CT dorkifier, resulting in crankulator lifting. The resulting steam issuance, fogged the glass over the tripulator, resulting in breakage of the optical path, so that the tripulator is donkified.

Replace the opernator with someone who knows how to properly diagnose the circuit.

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7

Re: Differential Relay Tripping

08/25/2016 2:27 PM

Just get rid of that pesky differential relay.

Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#8
In reply to #7

Re: Differential Relay Tripping

08/25/2016 3:15 PM

Are those UL rated?

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#12
In reply to #8

Re: Differential Relay Tripping

08/25/2016 8:07 PM

Rating? Rating! We don't need no stinking UL rating.

We are LynDoor™Industries.

We only make the best. The very best. You will never find a better .............whatever.

Those other stupid rating services are bad, really bad. None worse anywhere. People are saying that the others are crap and LynDoor™Industries is the best! The very best in the entire, whole, complete, only solar system.

I saw thousands of people dancing in the streets, with my own eyes, on TV and they are chanting LynDoor...........LynDoor..............LynDoor..............LynDoor.......LynDoor

Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#13
In reply to #12

Re: Differential Relay Tripping

08/26/2016 10:17 AM

Somebody needs to hide the Trump Kool-Aid from this guy!

Next thing you will be saying Lyn-Dor Industries Mission Statement is "Make America Great Again".

I just want one that says "America First and Forever".

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#14
In reply to #13

Re: Differential Relay Tripping

08/26/2016 3:00 PM

Since you mentioned it, Herr Drumpf's motto is really "Make America Hate Again".

Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#15
In reply to #14

Re: Differential Relay Tripping

08/26/2016 4:06 PM

I am sorry you feel that way. I really do not think it will be that way. I expect people can find common ground across the board, work together, and continue to improve this country. It stops when groups stop repeating patterns that leaves them out of the dialogue, interferes with their productivity and prosperity, or that results in illegal activities that get them into problems.

Law is intended to be the final authority in this country. Since when are some people exempt from obeying the law, or from the consequences of breaking the law? There are supposed to be NO class distinctions here in this country, and if there are, they need to be uprooted.

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#16
In reply to #15

Re: Differential Relay Tripping

08/26/2016 6:17 PM

I refuse to discuss this any further.

Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#10
In reply to #7

Re: Differential Relay Tripping

08/25/2016 4:52 PM

I should have thought of that myself. Here at insubordinate power and light, we use small jumpers on many things just to keep it all running - NO MATTER WHAT.

If you believe that, I can broker a deal on Lyn's dream home in Az.

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
2
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#9

Re: Differential Relay Tripping

08/25/2016 3:51 PM

A transformer differential current relay should only trip for a fault within its zone of coverage (within the transformer). If it is tripping for a current outside the zone of protection, the first suspect is that one of the sets of CTs is wired in reverse. At low currents, it may not trip for transformer energization, especially if the harmonic restraint is working correctly. So first thing, double-check that the CTs are wired EXACTLY as the relay's instruction manual specifies.

Other possibilities include:

- CTs that were specified with the wrong ratio or set on the wrong tap, so that the starting current of the motor drives them into saturation, leading to incorrect secondary current to the relay.

- CTs that were specified with too low an accuracy class, so that they do not provide true secondary current at high primary current.

You haven't told us what type of differential relay you are using, any specification of the transformer (voltages, winding configuration, rating), CT ratios and connections, or a schematic of the protection scheme. It is hard for us to diagnose something that is invisible to us.

__________________
To get the right answers, first you need to ask the right questions.
Reply Good Answer (Score 2)
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#11
In reply to #9

Re: Differential Relay Tripping

08/25/2016 4:55 PM

Nah, he has the reverse end of the discombobulator connected directly to the boiler fire eye, instead of the cat's head.

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#17

Re: Differential Relay Tripping

08/27/2016 4:17 PM

You have not made it clear if the CTs (of one phase) connected to the differential relay have only the transformer between them or both the transformer AND the motor.

Nor have you told us the relay type, transfo ratio, CT ratios etc.

To avoid false tripping, Differential relays have to cope with the problem that at high overcurrents, one of the two CTs with equal primary currents may saturate before the other - giving unequal secondary currents exceeding the "differential" causing a false trip.

When a transfo is protected, the CT ratios may not perfectly match the protected transfo ratio. There is the additional problem that the primary inrush current of the transfo only goes through the primary CT but not the secondary CT, always giving a differential current. There are similarities between the inrush current of a transfo and that of a motor but it does not follow that the differential relay tolerates both without a false trip.

The simplest reason for the tripping, if this is a new installation, is that the relay/CT system is wrongly connected, was wrongly designed or you have not used the designed relay settings.

If it is a proven installation, it may be a motor fault.

If you have taken a risk and bypassed the relay (during starting) to prove that the motor runs OK with relay active once it has started, it would have helped if you told us that.

Reply
Reply to Forum Thread 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

67model (1); Brave Sir Robin (1); IdeaSmith (1); James Stewart (5); lyn (4); PeterT (1); RAMConsult (1); Rixter (1); SolarEagle (2)

Previous in Forum: Use of Microcontroller for this Application   Next in Forum: Saturation of Current Transformer

Advertisement