ISF & Accuracy Class Of Current Transformer

09/14/2016 2:39 AM

Few customers, consultants are demanding CTs with low ISF & high accuracy.

But we know that saturation flux density & operating flux density are responsible for ISF of CT. But my question is when CT ratio is low how both ISF & accuracy class could be maintained i.e. low ISF & high accuracy!

Is it at all possible? If yes how the design is made ?

or it is an oxymoron?

Kindly enlight.

__________________
Enjoy the question till you get the answer
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: ISF & ACCURACY CLASS OF CURRENT TRANSFORMER

09/14/2016 3:31 AM

You could have asked this question of the equipment supplier when you were discussing solutions to your failed one. Why didn't you do that then?

__________________
Good moaning!
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: ISF & Accuracy Class Of Current Transformer

09/14/2016 9:36 AM

Prayer?

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: ISF & Accuracy Class Of Current Transformer

09/14/2016 11:42 AM

If what your customer wants is not available, then he has to pay somebody to design it....If he's not willing to do that then they must work with what is available....Your job is to tell them what is available...or design something yourself...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: ISF & Accuracy Class Of Current Transformer

09/14/2016 8:20 PM

I would say it is possible but you need to talk with CT manufacturers and suppliers for a possible solution and how much of a premium it will cost.

Does the CT ratio have to be low? Perhaps there is another way around the problem.

__________________
jack of all trades
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#5

Re: ISF & Accuracy Class Of Current Transformer

09/15/2016 2:50 AM

Interesting question. True, High accuracy and low ISF are seemingly contradicting requirements for a metering class CT. I have seen such CTs in existence but not aware of the design intricacies.

Hope some experts on CT design would care to clarify.

__________________
Raghunath
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: ISF & Accuracy Class Of Current Transformer

09/15/2016 4:13 AM

<...Hope some experts on CT design would care to clarify...> Quite. There are plenty of them at the CT equipment manufacturers' facilities, and they are more likely to respond to telephone calls rather than CR4 postings.

Phenomenon: the amount of use of telephones seems inversely proportional to the number of them in existence.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Aug 2016
Posts: 32
#7
In reply to #6

Re: ISF & Accuracy Class Of Current Transformer

09/16/2016 3:09 AM

ISF is the ratio of saturation flux density & operating flux density. In low ratio CT say 50/1A , due to low operating flux density the ratio will be high means ISF will be high. Thats' why I have raised my query whether low ISF & HIGH accuracy are possible in low ratio CT or not !

I just wanted to know from a renowned forum like this as design feasibility was my doubt.

I shall go to vendor or for telephonic discussion after this.

__________________
Enjoy the question till you get the answer