Restricted Earth Fault Protection at Delta Side

09/22/2016 1:19 AM

We are habituated to use REF protection at the "Y" side of the transformer whose neutral is either solidly ground or resistance ground & ultimately during the fault within the zone the delta side breaker to be isolated.

Recently few consultants are asking to provide REF protection at Delta side also. Now my questions are as under:

1. Is it really a REF to be called as there is no neutral CT for biasing?

2. Instead of REF can we call it high impedance balance earth fault ?

3. How the relay settings vary from "Y" & Delta or both can be same?

4. Any other information with you?

Kindly throw some light.

__________________
Enjoy the question till you get the answer
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Restricted Earth fault Protection at Delta side

09/22/2016 3:27 AM

There's a page in Wikipedia about earthing systems, Matey. Come back when you've read it.

__________________
Good moaning!
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Restricted Earth fault Protection at Delta side

09/22/2016 3:32 AM

We don't do homework!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#3

Re: Restricted Earth fault Protection at Delta side

09/22/2016 5:30 AM

Once you've read about earthing systems, you need to put "restricted earth fault" into any internet search engine, and read on. Come back if there's anything else you need.

__________________
Good moaning!
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4

Re: Restricted Earth Fault Protection at Delta Side

09/30/2016 5:29 AM

See [for instance]:

file:///C:/Users/user/Downloads/TGN%20Restricted%20Earth%20Fault%20v1_0.pdf

You may use also a Split Core Current Transformer

See [for instance]:

https://www.accuenergy.com/product/acuct-r-split-core-ac-current-transformers?campaignid=295804400&adgroupid=22202342000&creative=119117734280&adposition1t1&keyword=%2Bsplit%20%2Bct&matchtypeb&device=c&gclid=CJScmNLhts8CFasNcwode3MKcQ

__________________
Julius
Register to Reply