Star-delta Connection

09/22/2016 7:31 AM

dear all

good day

in our station plant we have two motor 400V ,37KW , one connected to air compressor and the other one

connected to water pump,the motor for water pump connected directly ,but motor for air compressor connected

across star-delta connection, Why is there a difference in connection long as the motors have the same power,

also On what basis be chosen connecting the motor (star-delta or directly)

thanks for all

Register to Reply
Pathfinder Tags: star-delta connection
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: star-delta connection

09/22/2016 8:06 AM

One possibility is that the supply for the compressor is not resilient enough to go direct-on-line without dragging down the supply volts to other equipment on the same supply.

Another is that the inertia of the compressor is too large for the motor to get away on direct-on-line.

There may be other reasons, historical, for instance.

The only way to find out for certain is to ask your local, friendly, Electrical Engineer.

__________________
Good moaning!
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Star-delta Connection

09/22/2016 11:47 AM

Possibly the start and stop frequency of the compressor, was the determining factor...

http://electrical-engineering-portal.com/comparision-of-direct-on-line-dol-and-star-delta-motor-starting

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#3

Re: Star-delta Connection

09/22/2016 12:06 PM

Why is there a difference in connection long as the motors have the same power,

Just because they have the same rating, doesn't mean that they are drawing the same power at any given time.

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Star-delta Connection

09/22/2016 12:50 PM

The compressor almost surely has greater rotational inertia than the pump.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Star-delta Connection

09/22/2016 5:55 PM

The duty cycle might also make a difference. the pump may only turn on once and stay running for a long time, whereas the compressor starts and stops a lot during the same time period.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#7
In reply to #5

Re: Star-delta Connection

09/25/2016 10:47 PM

A frequent duty cycle with a reduced voltage start will create more rotor heating, shortening the life of the equipment. The time during which the motor rotor is turning slower than design stator speed operating at design frequency results in excess rotor heat.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#6

Re: Star-delta Connection

09/25/2016 10:32 PM

There are some incorrect conclusions presented in this citation, such as savings on cable sizes. Ridiculous in normal industrial environments.

Depending on the type of water pump and type of compressor, the required starting torque for the equipment is likely the reason for the application of one of the other.

Perhaps you have a positive displacement pump, and a centrifugal compressor, in which case the starting application might make some sense. Otherwise I find it bewildering to see the application of reduced voltage starters for any modern electrical system, you add more clap trap and failure points than ever actually needed in a reasonably well designed power system.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#8

Re: Star-delta Connection

09/29/2016 8:56 PM

Star delta reduces the current demand on the supply, but star connection reduces standstill torque a lot compared to delta - it could only be used on a relatively easy to start load.

It may be it was a standard compressor unit and the supplier did it that way because most customers do not want a heavy demand to upset their supply.

Possibly, your plant may start both motors together automatically and limits on your supply dictated a reduction of maximum demand.

Since you have not given your supply capacity and what other motors or other loads you have, this can only be a guess.

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); Crabtree (1); JRaef (1); Mikerho (1); rwilliams (2); SolarEagle (1); Tornado (1)