ElCid vs Loop Test On Generators?

10/10/2016 12:31 PM

Hey engineers!

Which test you prefer for condition monitoring or as a factory test?
Elcid uses only 4% flux and measures mA.

Loop uses around 100% flux and measures temperature.

I have used ElCid couple times, and never loop test, because it's is heavy to do.

I know that ElCid can see couple things that loop test can't, but can loop test see something that ElCid doesn't? Will I miss something if I only do ElCid as a factory quality test?

In best way you do both of them, but it is not often possible.

So what are your thoughts?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#1

Re: ElCid vs Loop Test On Generators?

10/10/2016 3:11 PM

This guy?

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: ElCid vs Loop Test On Generators?

10/10/2016 4:01 PM

Yes. Everything the loop test would tell you that the other one doesn't.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#3

Re: ElCid vs Loop Test On Generators?

10/10/2016 5:24 PM

Your two tests "Elcid" and "loop" do not ring any bell's in the old memory - except the Spanish hero (El Cid - movie, Charlton Heston?).

From what you write

  1. "Elcid" is a low voltage & current test, cold static Machine??
  2. while "loop" may be where you run the generator into a full voltage load (Grid?) at zero power factor lagging.

The second test can push stator and rotor currents to maximum rated values at rated voltage/speed and reveal excessive temperature rise or mechanical contact at full expansion, if run a long enough time. Obviously this is a more thorough test but takes more tester time, testgear and electricity.

Test 1 is a cheaper option, but is only meaningfull if you know for certain the relation of the measurement to full voltage/current tests, that is you have tested a number of similar machines at full/voltage current as well as "elcid" and can have a view based on experience.

Essentially, test 1 can tell you the iron is OK and you have about the right number of winding turns, it does not show much about rotor state (unless you can do an open & shorted rotor test and turn the rotor slowly through 360 degrees) - it would not tell if the wire was too thin or the cooling fan mounted the wrong way round! Test 2 is obviously more comprehensive.

Register to Reply Score 1 for Good Answer
4
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#4

Re: ElCid vs Loop Test On Generators?

10/11/2016 5:37 AM
__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Good Answer (Score 4)
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#5
In reply to #4

Re: ElCid vs Loop Test On Generators?

10/11/2016 8:31 AM

Thanks JohnDG for the paper references - they explain the tests pretty well.

I have done loop tests on generator stators after repairs & rewedging, and it is great for spotting defects in the insulation and wedging. You can look for the defects (evident as hot spot in real time with an infrared imager. However, as the OP stated, the test is laborious to set up since you need to induce a significant loop current through the test setup. We used a 2400V contactor and HV cables fed from an aux supply to run several hundred amps through the loop. It took a day to set up, a few hours to do the test, and then the rest of the day to tear down.

I haven't used the EL-CID test method, but from what I can gather, it can only give you part of what the loop test can. It can be set up more easily and quickly, but you trade that off for less information.

In my book, if you want the better test, do the loop, but if you don't have the time and resources, do the EL-CID. I would also recommend a Doble insulation power factor test on the stator insulation, with RIV (radio interference voltage) measurements. It can point to issues with the overall stator insulation such as moisture problems, end turn issues, and general insulation deterioration.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#6

Re: ElCid vs Loop Test On Generators?

10/12/2016 6:14 AM

With my experience, I would say that ELCID detects even smallest shorts which in fact may not be a hot spot if checked with loop test. Here exception would be core end packets which are stepped. normal moving prob would not cover these packets and held held probe would be used individually on each tooth of each packet. Here the accuracy may not be that good. Except for this limitation, if the results are acceptable (within acceptance norm) then loop test would not be necessary. However, if ELCID shows peaks beyond limit, then loop test is a must to see how it behaves from thermal consideration and acceptance norms for loop test would prevail.

Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: