Anonymous Poster #1

PT Connection

11/29/2016 5:50 AM

What type of PT configuration is this?
1. I cannot understand why A-phase of the secondary Delta winding
of PT and B-phase of star winding are grounded.
2. Why Primary and secondary neutral have separate winding?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: PT Connection

11/29/2016 7:07 AM

The individuals who drew, reviewed and approved the installation for construction should be in the various boxes in the corner of the drawing. These would be the best people to ask.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Off Topic
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: PT Connection

11/29/2016 9:05 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#3

Re: PT Connection

11/29/2016 10:37 PM

The drawing are not drawn professionally really can see which is primary winding and which is secondary winding

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: PT Connection

11/30/2016 3:27 AM

The question has already been answered for you on another website.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#5

Re: PT Connection

12/01/2016 12:22 PM

1. PT secondarys are always earthed - as part of keeping xxxkV from LV equipment and you. Capacitance coupling to unearthed secondary from HV primary is enough to be lethal, particularly since current in normal conditions could exceed "let-go" hand potential. Which phase is earthed would be just convention.

2. The neutral has a separate PT. My opinion is that the interconnection of the 4 PT secondaries is a) the same as that of primaries, plus it gives "zero sequence" voltage, "positive & negative sequence" voltage and 3 line voltages to earth separately in LV circuit.

3. the lower secondary of the 0-X0 PT primary may be because the PTs have two secondaries any how; opposite polarity might be required - note obvious cross-over of secondary connection; or maybe diffferent voltage required.

4. As has been commented, the manufacturer or the protection relay drawings and types or maintenance manual may help.

Reply