failure of ac equipments

08/11/2007 5:14 AM

Hai every body

I am an electrical engineer .I wm working on 66/11 kv substation 66 kv side is GIS and 11 KV was VCB breaker .Transformer 25MVA 11 kv side with earthing transformer 11kv/415v we are getting auxilary supply from earthing transformer. My problem was when 11kv out going feeder trips on e/f relay my auxiliary supply equipments getting some high voltage /current damaging my equipments like electronic cards , ac contactors & annunciators .I checked transformer neutral earthing also rigidly connected to ground and Iam getting P-N 230v and P-P 440 volts .

is there any reason for the above please help me regarding this .If you need any more details contact me thru CR4 or my mail ikarthik77@rediffmail.com

expecting suggestions from our members

bye

karthik

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member Hobbies - Musician - New Member Engineering Fields - Mechanical Engineering - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member Hobbies - Fishing - New Member

Join Date: Mar 2007
Location: South-east corner of Spain 50 48 49.24N 2 28 27.70W
Posts: 1508
Good Answers: 31
#1

Re: failure of ac equipments

08/11/2007 6:17 AM

HAVE YOU GOT A CIRCUIT DIAGRAM? OR CAN YOU DO A QUICK DRAWING IN PAINT JUST SO WE CAN SEE WHERE ALL THE CONECTIONS ARE? SOUNDS LIKE SURGE TRIPPING CURRENT IS GETTING TO THE CARDS BEFORE TRIPPING THE TRIP! COULD YOU NOT CONNECT YOUR AUX STUFF TO THE LV SIDE OF THE TRANSFORMER? I'M WONDERING WHAT 11KV WOULD DO TO A 230V CARD, INTERESTING! DID YOU TEST THE EARTH? THERE IS A 3 PRONGED METER, ONE TO THE EARTH TERMINAL IN THE TRANSFORMER INSTALLATION, ONE 5M AWAY ON A PIKE IN THE GROUND AND ONE ABOUT 20M FROM THE FIRST! YOU NEED TO CHECK THAT YOUR GROUND IS WORKING! ITS NOT JUST THE CONNECTION TO THE TERMINAL THAT HAS TO BE GOOD, BUT THE EARTH ITSELF!

__________________
“It's kind of fun to do the impossible.” Walt Disney
Reply
Associate

Join Date: Nov 2006
Location: Chennai - India
Posts: 29
#2

Re: failure of ac equipments

08/11/2007 8:10 AM

It may be due to EMI problem,

we can solve it very easily using EMI filter, But its very costly and design a good EMI filter is an art.

Second way is we can isolate our electronic system from electrical system completely by using Battery power (it is a best method), other-wise use 230V UPS with different lines, or use A Small Generator - Kerosine driven is best for it for Electronic systems.

If you sure that its not because of EMI problem, Then we need circuit diagram for annalysis.

__________________
Every Problem has its own solution
Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#3
In reply to #2

Re: failure of ac equipments

08/15/2007 2:07 AM

UPS is OK-rather most desireable

At UPS Input you need to fit

  • Overvoltage Protection MODULE
  • +fast acting tripping MCCB
  • + Warning relay operated by the bypassing current from this Overvoltage Protection MODULE .
Reply