Surge Arrestors

01/03/2017 9:09 PM

How to go about selection of Surge arrestors in EHT systems like 110KV system.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Surge Arrestors

01/03/2017 9:15 PM
Register to Reply Good Answer (Score 3)
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Surge Arrestors

01/03/2017 10:30 PM

You hire someone who knows how to perform an Insulation Coordination Study. This is not a trivial exercise since an error or omission anywhere in your data will place your entire system at risk.

The output of the study will include such things as the BIL (Basic Impulse/Insulation Level) of each component, the Switching Surge Withstand, the Full Wave Withstand, and the Chopped Wave Withstand, the Switching Surge Protective Level, Impulse Protective Level, Front-of-Wave Level, along with arrestor ratings including Voltage Class, MCOV (Maximum Continuous Operating Voltage), TOV (Temporary Over Voltage), and will consider the type of system grounding, soil conditions, protective relaying, etc., etc.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)