Dear all
good day
please what is different between field voltage regulator and field current regulator in
automatic voltage regulator (EX 2100) and how can to control one without the other.
thanks for all
Pathfinder Tags: field regulator
Re: field regulator
01/12/2017 5:03 AM
Re: Field Regulator
01/12/2017 7:03 AM
Ac voltage can be regulated using this buck & boost scheme
2)Capacitors
Current Regulation
1) Inductors
That's the ABC's.
Get it from a legitimate technical university or technical school near you. Except if you have an IQ of 145~175, most likely, you can do it your own.
Register to Reply Off Topic (Score 11)
Re: Field Regulator
01/12/2017 4:02 PM
You are making a comment on somebody else's IQ, why???
Re: Field Regulator
01/12/2017 10:43 PM
IQ envy.
Re: Field Regulator
01/13/2017 12:49 AM
No, offense, I believe everybody has its own set of talents and aptitude in the sense that they are unique. It's like a pyramid, you know, as it was structured, every person is important irrespective of IQ.
IQ can be increased eventually by learning new things and accumulate much learning through time.
Re: Field Regulator
01/12/2017 8:54 AM
Maybe this explains it:
pdfstream.manualsonline.com/7/7079df42-4464-427b-b181-4496e6281f13.pdf
page 2-21:
"Field Voltage and Current Regulators - FVR & FCR The Field Voltage Regulator (FVR) is the typical manual regulator supplied on most applications and uses the generator field voltage as the feedback input. While FVR does permit the current to vary as a function of the field resistance, the FVR makes the manual regulator completely independent from the over excitation limiter. FVR uses the voltage from the generator field as feedback, with a setpoint from the MANUAL REF block. A PI regulator with integral windup protection generates the output. During operation in AVR mode, the output of the AVR is passed directly to the FVR output with no signal conditioning. On units that operate with an inner field voltage regulator loop such as compound exciters and some high ceiling exciters, the FVR uses a setpoint from either the AVR or the MANUAL REF block, and is always operational whether in manual or automatic operation.
The Field Current Regulator (FCR) is a special application of the manual regulator and uses the generator field current as the feedback input. The current setpoint is generally switched between a high level and lower level to provide transient forcing capability as well as steady state operation within the capability of the generator. Generally the setpoint is larger than expected field currents and the integral preset is operational. The FCR output is held at positive ceiling until enable becomes true which allows the output to follow the P+I regulator. The bridge firing command is the smaller of the FVR and FCR outputs. While it does regulate constant field current over varying field temperature, FCR is not the standard manual regulator."
Re: Field Regulator
01/13/2017 9:01 AM
Both regulators control the same quantity, magnetic coupling between rotor & stator, just different sensing methods. In both cases, the field is supplied with the same power.
It looks like the controller switches automatically depending on power system conditions.