UPS

01/11/2017 10:22 PM

Hi ,

when main source to ups turn off,ups take over rcd at DB trip.

please kindly help.

thanks.

chew

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#1

Re: ups

01/11/2017 10:57 PM

is that all the information you can give?

__________________
High Tolerance is Beautiful
Register to Reply
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: ups

01/11/2017 11:06 PM

The RCCB should be installed before the UPS in the Circuit Breaker panel, if the UPS causes it to trip, it means the leakage current inside the UPS is exceeding the trip current allowed by the RCD...so check the leakage of your UPS unit and the size of your RCD....one is probably at fault...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 2)
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#4
In reply to #2

Re: ups

01/11/2017 11:12 PM

you got all that from that?

__________________
High Tolerance is Beautiful
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6
In reply to #4

Re: ups

01/11/2017 11:23 PM

Just spitballin'....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#9
In reply to #4

Re: ups

01/12/2017 12:57 PM

I think SE really is Cleo.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#10
In reply to #9

Re: ups

01/12/2017 4:05 PM

...haha

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Active Contributor

Join Date: Jun 2009
Posts: 23
#3

Re: ups

01/11/2017 11:09 PM

Hi jerlyn

It is an online ups.

When we turn off the ups incoming to let the battery take over .

It trip the output supply rcd .

Thanks

Register to Reply
3
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #3

Re: ups

01/11/2017 11:22 PM

..."Some UPS units (particularly smaller cheaper units) don't produce a very accurate sine wave - in fact they are pretty awful, but do the job in hand and are good enough to drive the IT equipment connected to them. However sensitive things like RCDs etc will not tolerate them and do what yours is doing - switch off.

Another option is relating to the connection of the supply/inverter and earth in the ups. Under normal conditions the RCD relies on an imbalance in the L-N conductors due to electricity taking an alternative path back to the source - through the earth/CPC/person etc. This works due to N and E being joined to complete that path. Inside your UPS the inverter may not have a connection to the earth at all. This will allow an induced voltage to appear between N & E which some RCDs can detect - probably the ones with an earth tail. It also means that when the UPS is under operating load (from the batteries) the RCD is unlikely to function as intended. "...

http://www.theiet.org/forums/forum/messageview.cfm?catid=205&threadid=55339

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 3)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#12
In reply to #5

Re: ups

01/13/2017 4:50 AM

GA

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#14
In reply to #3

Re: ups

01/13/2017 5:09 PM

It may be one particular load.

Isolate all loads. Put system onto battery power.

Switch on each load in turn.

Energising a certain load may be found to cause trip. Check energising that load on its own without other loads.

You might find you do not need any loads to cause a trip, just cable capacitance!

While 50/60Hz fundamental currents may not exceed RCD trip current on mains sinusoid power, harmonics 3rd,5th etc will pass more current through capacitance. Basic inverters give out rectangular plus & minus pulses with high harmonics.

Splitting the load between several RCDs may solve problem. Perhaps RCD at each power outlet socket, with high operate current RCD, 100mA or more at UPS outlet.

Since you gave no kVA/volts/amps for UPS or description of load connections, I can suggest no more.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7

Re: ups

01/11/2017 11:24 PM

Something is not right. If the main source turns off, where is the current to trip the RCD coming from?? I suspect you have some large motors or capacitors on circuits in your DB which are backfeeding the panel and your UPS in an unbalanced fashion, which fools the RCD.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: ups

01/12/2017 2:49 AM

The RCD trips because the vector sum of the live and neutral currents downstream of it exceeds its trip setting, inferring that this level of current is flowing in the earth conductor.

Look in particular for (an) inadvertent connection(s) between neutral and earth downstream of the RCD. Once de-energised, a multimeter, some effort and some patience is all that is needed to find it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #8

Re: ups

01/13/2017 4:15 AM

<...this level of current is flowing in the earth conductor...> ...which might be formed by a human being.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#13
In reply to #11

Re: ups

01/13/2017 8:53 AM

similar to an ungrounded 220v heater...

Register to Reply Off Topic (Score 5)
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); Andy Germany (1); Brave Sir Robin (1); JE in Chicago (2); PWSlack (2); RAMConsult (1); rwilliams (1); SolarEagle (4); soon1 (1)

Previous in Forum: Feeder Pillar-Tennis Court Lamps   Next in Forum: Field Regulator

Advertisement