Valid question, newbies and pros(?) often confuse the alternator rating (250MVA@0.8pf), with the prime mover operating point (250MW).
The answer is it depends the rating of the prime mover and its ability to produce 250MW continuously; the alternator doesn't care as long as the operating point is within the GCC (Generator Capability Curve) and stability/voltage limits set by the system operator.
__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
GA from me too. I initially thought the answer was No but you convinced me!
But not sure why you say in 1st sentence "....prime mover operating point (250MW)" As you say later, we don't know the prime mover power, except that it's not < 200MW.
__________________
Give masochists a fair crack of the whip
That was a direct response to his query about loading the machine to a particular MW output. The shorter answer would be, "Assuming a fixed frequency, within its mechanical, electrical, and connected system limits, you can load your machine to any combination of MW, MVAR, and PF; but you can only choose any two out of the three."
__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.