D.G. - P.F.

08/17/2007 4:03 PM

Why we does not use capacitor bank while D.G. running

__________________
TARGET - Where many stop thinking, some start from there. Tenacity to get target helps to WIN.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#1

Re: D.G. - P.F.

08/18/2007 12:19 AM

D.G. = ????

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#3
In reply to #1

Re: D.G. - P.F.

08/18/2007 11:52 AM

DG = Deisel Generator?

Register to Reply
Commentator

Join Date: Aug 2007
Location: INDIA
Posts: 58
#4
In reply to #1

Re: D.G. - P.F.

08/18/2007 2:28 PM

Diesel Generator

when we start plant on D.G. that time we Tripp the Capacitor bank. if we does not tripping bank than our main supply incomer Air Circuit Breaker Tripp.

__________________
TARGET - Where many stop thinking, some start from there. Tenacity to get target helps to WIN.
Register to Reply
Commentator

Join Date: Aug 2007
Location: INDIA
Posts: 58
#5
In reply to #1

Re: D.G. - P.F.

08/18/2007 2:30 PM

Yes Diesel Generator

when we start plant on D.G. that time we Tripp the Capacitor bank. if we does not tripping bank than our main supply incomer Air Circuit Breaker Tripp.We can not improve d.g. p.f.? Our D.G. is 1000 KVA & P.F. is 0.80p.f.

__________________
TARGET - Where many stop thinking, some start from there. Tenacity to get target helps to WIN.
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#2

Re: D.G. - P.F.

08/18/2007 7:02 AM

You are using Capacitors when the EB supply is on probably because of Low PF.However with Diesel generating set the PF is normally 0.86 and hence u are not connecting the capacitor bank.If PF Is low with DG supply on then u need to use the capacitor bank .I presume you are using a centralized capacitor bank.If Individual capacitors are used on each equipment it may still be used .Other reason could be u may be using a HT capacitor bank centrally and DG being LT it may be cut off .Any way whether DG Or Mains supply PF determines use of capacitors.U may have to give more details to go in Depth

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Commentator

Join Date: Aug 2007
Location: INDIA
Posts: 58
#6
In reply to #2

Re: D.G. - P.F.

08/18/2007 2:42 PM

Thank You For replying

Sir actually we have 1000 KVA D.G. When we start the plant on D.G. that time suppose we does not Tripp the capacitor bank than our main Air Circuit breaker tripped so we always off the bank when our D.G. started. & its see in many company's they also doing like that.

__________________
TARGET - Where many stop thinking, some start from there. Tenacity to get target helps to WIN.
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#7
In reply to #6

Re: D.G. - P.F.

08/19/2007 3:35 AM

Does your DG come up to speed then transfer onto the system?

If so, and there will be a significant inrush to the caps.

Register to Reply
Associate

Join Date: Aug 2007
Location: New Delhi, India
Posts: 33
#10
In reply to #6

Re: D.G. - P.F.

08/20/2007 7:12 AM

We use capacitor banks to improve the power factor. These banks are connected in parallel to the supply at mains OR can be connected with individual inductive load. Usually connected at mains. These operate with automatic PF corrector relay which senses the pf & accordingly operates the capacitor banks to improve the pf. Capacitors draw leading current & are capacitive load on the system. These should never operate on DG as this will be an additional load to DG. Thus you would not be able to utilize full output of DG. The PF of DG set can be improved through an AVR. If you trip your Capacitor bank on DG supply manually, then you can get your control wiring changed so that whenever you run a DG set, capacitor bank will not come into play. It will only operate on State electricity.

Hope your querry is solved

Ashish Gupta

__________________
Ashish Gupta
Register to Reply Off Topic (Score 5)
Associate
India - Member - New Member

Join Date: Mar 2007
Location: India Bangalore
Posts: 40
#8

Re: D.G. - P.F.

08/19/2007 11:04 PM

Alternator of Diesel Generators systems are rated for 0.8pf Lag. We can not add uncontrolled reactive ( Capacitive ) compensation for DG. If in case of power factor of system goes to leading, then there is every chance failure of windings. hence usually all capacitor banks will be provided electrical interlocks to protect the DG.

Pls note that kW output from the DG is at 800kW, Only we can get the KVA benefit

if we add capacitors. Detailed study of the system is very important before we do take any changes in system.

__________________
Nothing is impossible, Impossible is nothing
Register to Reply Score 1 for Good Answer
Participant

Join Date: Sep 2007
Posts: 1
#11
In reply to #8

Re: D.G. - P.F.

09/28/2007 10:19 PM

What will be the effect of capacitor bank on DG engine. Will it overload the engine resulting in overheating / other problems.

Register to Reply
Anonymous Poster
#9

Re: D.G. - P.F.

08/20/2007 7:07 AM

We use capacitor banks to improve the power factor. These banks are connected in parallel to the supply at mains OR can be connected with individual inductive load. Usually connected at mains. These operate with automatic PF corrector relay which senses the pf & accordingly operates the capacitor banks to improve the pf. Capacitors draw leading current & are capacitive load on the system. These should never operate on DG as this will be an additional load to DG. Thus you would not be able to utilize full output of DG. The PF of DG set can be improved through an AVR. If you trip your Capacitor bank on DG supply manually, then you can get your control wiring changed so that whenever you run a DG set, capacitor bank will not come into play. It will only operate on State electricity.

Hope your querry is solved

Ashish Gupta

Register to Reply Off Topic (Score 5)
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard