Calculation of Connected Load

08/05/2017 2:27 PM

Is it possible to calculate connected single-phase load in mixed loaded SMDB by measuring amps?

Register to Reply
Pathfinder Tags: electrical
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Calculation of connected load

08/05/2017 3:10 PM
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Calculation of Connected Load

08/05/2017 4:57 PM

Yes from the main incomers , amps * volts = watts...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3
In reply to #2

Re: Calculation of Connected Load

08/06/2017 11:41 AM

"...amps * volts = watts...", only true for resistive loads (and DC circuits), otherwise power factor comes into play.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4
In reply to #3

Re: Calculation of Connected Load

08/06/2017 12:47 PM

He only asked if it was possible, not how to do it... but it's true the meter type, waveform and load characteristics may or maynot come into play in the accuracy of the measurement....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Participant

Join Date: Aug 2017
Posts: 2
#5

Re: Calculation of Connected Load

08/06/2017 2:53 PM

May be question not clear.

It is like this one MDB feeding both single phase load and Three phase load by measuring the incoming current using clamp meter, is it possible to find out how much single-phase load and three phase load connected to MDB .

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6
In reply to #5

Re: Calculation of Connected Load

08/06/2017 3:46 PM

It's not getting any clearer....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7
In reply to #5

Re: Calculation of Connected Load

08/06/2017 9:03 PM

No, you cannot determine how much current goes to the single/three phase circuits by simply measuring the three phase incomer current. The only way to do this is to measure the currents passing through each individual breaker pole, and this method will only work if there are no (hidden) single phase loads attached across any two phases of a three phase circuit once it leaves the MDB (Main Distribution Board).

If you suspect that there are single phase loads on the three phase circuits then you will have to disconnect/switch them off and take before and after readings on each phase.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Calculation of Connected Load

08/07/2017 3:11 AM

Yes.

A pocket calculator might come in handy.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#9

Re: Calculation of Connected Load

08/09/2017 2:44 AM

No. you can not measure single phase load from the SMDB. you can measure the Load in each phase. Switch off 3 phase loads, and then measure each phase so you will get single phase load

Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#10

Re: Calculation of Connected Load

08/16/2017 11:25 PM

Yes, by adding all the single phase load togeather

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Alanvaderi (1); lyn (1); PWSlack (1); RAMConsult (2); Simon Wan (1); SolarEagle (3); Thukkoji rao (1)

Previous in Forum: Distribution Transformer In Front of my House   Next in Forum: DC Motor - Sparking

Advertisement