FCU Blower pulling in water

09/03/2007 11:44 PM

Hi,

Recently i encountered a problem at our cleanroom. The FCU's blower for our return air is pulling in water and after a while it floods the ducts. We checked the coil and drip pan and they are wet but not to the extend of overflowing. What could be the problem?

Any help is appreciated.

Thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Safety - Hazmat - Environmental, Safety & Health Manager Hobbies - Musician - Theremin (That about says it all...)

Join Date: May 2006
Posts: 289
Good Answers: 19
#1

Re: FCU Blower pulling in water

09/04/2007 10:20 AM

alvinccfei,

A couple of observations/questions:

If I understand the situation, You are operating a clean room with a supplemental fan-coil unit that recycles air from the room itself.

What ducts are being flooded?

Does this FCU have a ducted supply of air in addition, or is it operating solely to provide thermal comfort, by constantly recycling the air in the room?

Is it possible that the fan is operating at too high a speed, causing condensed moisture to blow off the coils, or out of the condensate pans?

What is the temperature of the chilled water serving the FCU? If too cold, it could cause excessive condensation.

What is the moisture content of the air being supplied to the clean room via the primary HVAC/HEPA air filtration system ?

Is the R.H. in the clean room controlled to manage ESD?

Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2

Re: FCU Blower pulling in water

09/04/2007 5:00 PM

restricted air flow.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Active Contributor

Join Date: Jun 2007
Posts: 10
#3

Re: FCU Blower pulling in water

09/04/2007 11:27 PM

Hi JMAN,

Thanks for the reply.

Yes, the FCU is use for the return air (recycled air). The ducts that were flooded were the ones after the FCU where the recycled air is directed to the plenum.

The FCU does not have other air supply apart from the reycled air. I'm not sure if the fans are running at too high a speed but from what i see the fans are pulling condenstate into the duct.

The room RH should be quite high as we are running a wet process in the cleanroom.

Hi ozzb,

May i know what you meant by restricted air flow?

Register to Reply
Anonymous Poster
#4

Re: FCU Blower pulling in water

09/05/2007 9:24 AM

up-flow coil in a down-flow application? or the other way around... The fins on the coil are slanted in the wrong direction. The air flow causes the water to blow into the ducts instead of dripping down to the pan.