Could some one please let me know fuctionalities of Buffer Tank and Expansion tank in an HVAC system.
I am a mechanical Engineer who has just joined a conpany in HVAC field.
Awaiting reply
Biju Mohan
Abudhabi
Safety - Hazmat - Environmental, Safety & Health Manager Hobbies - Musician - Theremin (That about says it all...)
Good Answers: 19
Re: Functionalities of Buffer and Expansion Tanks in an HVAC System?
09/05/2007 11:27 AM
bijumohan,
An expansion tank is typically used in a closed loop HVAC system. When the liquid (e.g., water, glycol, refrigerant, etc.) in the system is heated, the liquid will expand and the tank provides a place for the expanded liquid to go without allowing the resultant pressures to exceed the design of the system.
(Chilled Water) Buffer Tanks are designed for chilled water systems with insufficient water volume capacity, in relation to the chiller capacity. Relatively low water volume systems require additional "buffer" capacity for the system to eliminate problems such as excessive chiller cycling, poor temperature control , and erratic system operation.
09/05/2007 11:52 PM
Dear JMAN
Many thanks for the prompt reply. This is the first time I am using this site and let me tell you we are more than excited to have a dais to address and clear our technical doubts.
Once again many many thanks
Regards
Biju Mohan
UAE
09/06/2007 11:16 AM
Hi,
May I add some to Jman's comments
RGS
Ediri
09/08/2007 12:02 AM
Please go ahead Mr. Ediri69
09/08/2007 3:25 AM
Hi
As Jman Said, expansion tank will protect the system when liquid pressure trying to rise (above design pressures) due to high liquid temperature.
Not only that!!!!! Problems can occur when pumps are starting, stopping, valves closing and opening (specially ball valve). So all this liquid hammers and system piping jerk will eliminate by the expansion tank.
There are two type of Buffer tanks
  1. Close type
  2. Open type.
Close type buffer tank is typically use in a insufficient water volume close loop Chill water system. In the same system there will be a Expansion tank also.
Open type buffer tanks refer Mr Jman's explanation.
Thanks and regards,
Ediri
Fusble and motorized dampers
09/08/2007 4:13 AM
Many thanks Mr. Ediri
can you cast some light on two kind of fire dampers (fusible and motorized).
I posted this query in the forum before but the reply was not clear fully. Cud u please explain to me what is the criteria to decide whether to go for fusible or motorized dampers. which is more expensive and more reliable?
hope u can come up with an answer
rgds
biju
Engineering Fields - Piping Design Engineering - BALU
Re: Fusble and motorized dampers
09/21/2007 3:09 AM
You are learning HVAC through the forum. welcome
Should do some course on HVAC and also read more about hvac components
the fire damper
function of the fire dampers are to cutoff the air flow in a closed loop typically.
Fusible fire dampers:- The damper closes when the fuse is blown due to high temp of the air passing through this damper. Usually this happens when fire accident happens and the AHU is running. spring with a fuse is holding the open possition of the damper.
motorised dampers: Usually takes the input signal (digital/analogue) through a divice..... could be directly from sensors/ fire alarm system and cause to start a motor attached to the damper and make an effor to close the damper. there should be BAS (building automation system ) in place for use of such dampers or
may work with a stand alone controller
I hope you have got the answer.
sivabala
is that OK for U........xcomment
09/21/2007 11:49 PM
Many thanks Mr. Sivabala...
Yes.. I do want to do some course in HVAC, but the problem is I am in abudhabi working with archirodon and the management has given me an HVAC assignment in Ruwais (I was into thermal insulation before). Mostly this job would be subcontracted...still I should be conversant with the system, no?...
Would you permit me to clarify further queries in your email? please confirm