High Temperature for the excitation transformer

09/05/2007 5:47 AM

What makes the excitation transformer temperature to go high. Its rating is 11KV/415KV, I-21.5A, 50HZ, 410 KVA.Cooling - AN. The temperature rise is between 56-60 oC.At that temperature the Excitation field current is between 410-600. This is an excitation transformer for a hydro-plant gen.

Please give me the possible causes and measures, thnk you.

__________________
poy
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Participant

Join Date: Apr 2006
Posts: 1
#1

Re: High Temperature for the excitation transformer

09/06/2007 12:40 AM

Please correct your question. All the figures in you question are inconsistant. For an answer one needs to know the name plate data of 1) Excitation Transformer i.e. Rated kVA, Volatge, Current, Phases. 2) Excitation Rectifier i.e. Rated Input Voltage (1 or 3) Phase, Output Voltage and Current.

MIQ

Register to Reply
Power-User

Join Date: Aug 2007
Location: Heilonjang China. 2 blocks from you
Posts: 109
Good Answers: 5
#4
In reply to #1

Re: High Temperature for the excitation transformer

09/07/2007 9:10 AM

The voltage rating is 11kv/415V.

I- for current

3Phase.

__________________
poy
Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#2

Re: High Temperature for the excitation transformer

09/06/2007 8:50 AM

If the heat is significantly higher in one location, you may have a loose connection or shorted winding turn. If the heat is generalized over the entire unit, the problem is likely related to environmental or operating conditions. If available, a thermal imager (infrared thermometer) will help pinpoint a localized problem. In a pinch I've used a zero lux camcorder (it has an infrared filter for extremely low light conditions).

If the temperature rise is not in a specific location, I would check the following:

1. If the transformer is in a protective enclosure, check the cooling louvers and filters (if any) for dirt or other obstruction.

2. Look for a buildup of dust or other grime on the windings. This will act as an insulator and prevent proper cooling of the windings.

3. Is the Excitation transformer overloaded (compare the actual current on all input phases with the nameplate rating)?

4. Is the ambient temperature higher than the nameplate rating?

5. What has changed since the unit was operating at normal temperature?

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Commentator

Join Date: Jun 2007
Posts: 82
Good Answers: 2
#3

Re: High Temperature for the excitation transformer

09/06/2007 6:15 PM

Above 410, you have exceeded the device's rating of 410kVA. The average is certain to be above 410 kVA.

__________________
The purpose of a system, is what it does.
Register to Reply