Starting a 30kW Motor by Soft Starter

01/20/2018 10:22 PM

Hi;

We have a trim waste blower at Corrugator machine which has a 380V, 30KW, 4pole AC motor which drives an impeller by the mean of V-belts with double of motor speed. Previously motor was running by star delta starter. As we can not go beyond 6-7 start/stop per hour for such kind of load, so during normal operation of corrugator, if machine was stopped for some reason, trim waste blower was not stopped.

As we calculated that if we stop the blower on each machine stop and start on machine start, we can save energy. So we have installed soft starter 37KW Schneider ATS01N272Q. But we have observed that when blower is start, current goes up to 272A and remains the same for almost 3-4sec, after that current starts dropping and stays at 42A (motor coils connected in delta). The total time which blower takes from zero to max speed is around 6-8sec. We have set the initial voltage around 260v. We always used VFD to control the speed and never used soft starter, so dont have idea about correct operation of soft starter. So, please guide me on following points;

  1. Is above mentioned condition normal?
  2. How many times can we start/stop the motor in an hour by soft starter?
__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Starting a 30KW motor by soft starter

01/20/2018 10:43 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2014
Location: Hemet, Land of milk and honey.
Posts: 2365
Good Answers: 36
#2

Re: Starting a 30kW Motor by Soft Starter

01/22/2018 12:30 AM

92 pages is a lot of waiting, unless you're Evelyn Woods.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Starting a 30kW Motor by Soft Starter

01/22/2018 1:19 AM

Well just shooting from the hip, I'd say the amperage looks a little high, I would start by experimenting with raising the voltage levels, and at some point I would want to meg out the windings, you might need a redip...the insulation does wear out....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Starting a 30kW Motor by Soft Starter

01/22/2018 1:35 AM

1). Yes, that’s very normal.

2). A good soft starter neither increases or decreases the number of starts-per-hour that the motor can tolerate.

That however is NOT a good soft starter, that is a cheap soft starter. To make it cheap, Schneider only uses SCRs on two of the three phases, the center pole is just a bus bar. Although this method technically works, it is harder on the motor because it is inherently providing highly unbalanced current, so more of the current going into the motor is creating heat instead of torque. 6-7 starts per hour is not usually considered excessive, but it might be when using one of these cheap soft starters.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#6
In reply to #4

Re: Starting a 30kW Motor by Soft Starter

01/22/2018 5:32 PM

The longer it takes for your motor to get up to speed, the more heat you are putting into the rotor circuit. The 7 starts per hour is likely D.O.L. or across the line starting.

If you can give it more voltage and shorten the time, your motor will last longer, and you can get more starts per hour, up to 7, if the motor was designed to NEMA standards. This link points to the method US NEMA gives as design guides for motor starting, and does not factor in the additional heat added when the starting time is extended, however much that is (?).

www.landbelectric.com/download-document/78-maximum-nema-inertia-starts.html

Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #6

Re: Starting a 30kW Motor by Soft Starter

01/22/2018 7:12 PM

Common misconception.

Starting time is extended, but only because the starting TORQUE and thus CURRENT going into the motor is lower. If you were to plot the energy that goes into starting a motor from a dead stop to full speed as a curve with a soft starter or Across-the-Line / DOL, the area of that curve is exactly the same; instead of steep, high and and short duration, it is shallower, lower and longer duration. There is a net zero change in actual motor heating effect.

the only thing that changes that situation is a VFD, because the VFD can limit the starting current to 100% of the motor FLC, regardless of how long that may take to accelerate; 1 minute, 1 hour, 1 day, 1 week, etc.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#8
In reply to #7

Re: Starting a 30kW Motor by Soft Starter

01/22/2018 9:21 PM

That is true, the real work (kw) is the same over any time, but the heating of the rotor bars is a function of slip frequency and time. Many soft start manufacturers warn against extending the time to get to motor design slip speed, a common mistake when setting the starting voltage too low. Since most (induction squirrel cage) motors we see are rotor limited on start, stator winding protection will not catch rotor overheating until too late.

One rule of thumb, if the motor voltage is more than 10 times the horsepower rating, then the motor may not be rotor limited on start, like a 500hp 6900V motor.

Register to Reply
Power-User

Join Date: Aug 2007
Location: Lahore
Posts: 369
#9
In reply to #6

Re: Starting a 30kW Motor by Soft Starter

01/23/2018 3:20 AM

Hi rwilliams;

I could not understand your words

"If you can give it more voltage and shorten the time, your motor will last longer, and you can get more starts per hour, up to 7, if the motor was designed to NEMA standards".

Here if initial voltage is 235, the current rises up to 255A (FLA 55A) when i increase the initial voltage 250V, current rises up to 292A. More the current drawn, more the heat. Is it?

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#10
In reply to #9

Re: Starting a 30kW Motor by Soft Starter

01/24/2018 12:50 AM

The time running at less than rated slip speed will shorten significantly, that reduces the total heat.

These motors are designed to be started in a very short time, at a very high current. If you deliberately make the motor operate at slow speed by limiting the accelerating torque, the rotor bars will take higher current over time than expected, and you shorten the life of the motor, unless you take steps to limit the temperature rise.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Starting a 30kW Motor by Soft Starter

01/22/2018 1:58 AM

Depending on the features of the soft starter, it may be possible to save some energy, but only a bit. And you might save a bit on power factor, but again not much, and that's not the same as saving energy anyway.

If there are periods of time where less air flow is sufficient, you could save energy with a VFD.

Speed-up drives are ordinarily pretty silly. Just get a motor with the right number of poles.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Aug 2007
Location: London England.
Posts: 583
Good Answers: 10
#11

Re: Starting a 30kW Motor by Soft Starter

01/24/2018 6:47 AM

Are you really saving energy? Most big motors take a lot of energy to start up & levels out once it is running, A case in point is I used to work with four 1000cuft compressors and it was found to be more economical to leave them running all day & to "unload" them when the pressure was reached rather than stop and start them.

Bazzer

__________________
When I die I'd like to go peacefully in my sleep like my dad,not shouting and screaming like his passengers.
Register to Reply
Power-User

Join Date: Aug 2007
Location: Lahore
Posts: 369
#12
In reply to #11

Re: Starting a 30kW Motor by Soft Starter

03/18/2018 12:55 AM

Hi;

As I discussed earlier that I have installed soft starter Schneider brand "ATS01N272Q" which dont have built-in over load, so if we install regular thermal overload Schneider "GV3P 65 48-65A", it gets trip during starting time. The starting time of motor is almost 8-10sec and peak current goes up to 265A for 4-5sec then drops gradually. Kindly guide which type of thermal overload will be suitable for this application.

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#13
In reply to #12

Re: Starting a 30kW Motor by Soft Starter

03/19/2018 6:02 PM

you need to increase the voltage/current adjustment of the soft start to get the motor to start in a shorter time.

If you cannot do this, then a higher class of Overload Relay is required. However, the possible damage to the motor running it for 8 to 10 seconds close to locked rotor conditions is what you risk.

The motor designer can tell you the actual thermal margins built into the motor. This motor is likely rotor limited, so the damage curve for the rotor is what needs to be calculated, along with your duty cycle.

Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: