IEC Cable Sizing

02/06/2018 9:55 AM

NFPA 70 430.22(A) Branch-circuit conductors for a single motor, continuous duty, shall have an ampacity of not less than 125% of the motor’s full load current.So, Cable Ampacity > 1.25 x FLA x derating factors.

As far as I searched there is no 1.25 multiplier in IEC, Cable Ampacity > FLA x derating factors.

Is the above correct?, or there are some multiplier/margins for cable sizing as in the current project we are going use the cables which are manufactured according to IEC.

Register to Reply
Pathfinder Tags: IEC Cable Sizing
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Sep 2017
Posts: 76
Good Answers: 1
#1

Re: IEC Cable Sizing

02/06/2018 10:28 AM

I would also be curious to know the answer to this.

Please let me know

Thanks

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: IEC Cable Sizing

02/06/2018 10:37 AM
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#3

Re: IEC Cable Sizing

02/06/2018 1:45 PM

My experience is that IEC is much more "relaxed" than NFPA 70 (as are many regulations in Europe compared with NFPA).

We Americans like the overkill safety factor.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4
In reply to #3

Re: IEC Cable Sizing

02/06/2018 3:56 PM

“IEC is much more relaxed.”

It depends on where you are under the IEC banner. BS7671 is quite strict on earthing (grounding) requiring earth loop impedance testing and documentation, testing that the NEC doesn’t require.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#5

Re: IEC Cable Sizing

02/06/2018 5:06 PM

Down here in NZ we are mostly IEC.

We wouldn't be required here to oversize a motor feeder by 125%. The feeder would be dimensioned based on motor FLA and feeder length where appropriate. The cables that are used here are broadly the same csa vs amapcity as in NEC-land too.

Another key difference is in the circuit breakers. For a motor circuit, the preferred circuit breaker (for smaller motors which can be protected with miniature circuit breakers) is a D-Curve which trips magnetically at 5x - 10x rated current and so can buck motor starting currents better than the C-Curve which is used for most other loads.

__________________
paulusgnome
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: IEC Cable Sizing

02/06/2018 5:29 PM

If in doubt, consult a qualified local Electrician. To do otherwise invites the risk of a measure of unpopularity with the facility's fire insurance cover provider.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Hobbies - Musician - New Member Hobbies - Car Customizing - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2007
Location: FL Space Coast
Posts: 536
Good Answers: 14
#7

Re: IEC Cable Sizing

02/07/2018 6:35 AM

Talk to the AHJ, as in authority having jurisdiction. When it comes down to it, their opinion is the one that matters. If you are in the US, you will most likely fall under the NFPA guidelines, I would hazard to guess Canada (and maybe Mexico?) would be similar. Outside of the Americas, you will most likely will fall under IEC purview. I can tell you, opinions from the internet are worth exactly what you paid for them. Get in touch with the local authorities. They can guide you better than we can.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#8

Re: IEC Cable Sizing

02/08/2018 3:15 AM

Let's take an induction motor of 100 hp/460 V [122 A and 122*1.25=152 A]

and 75 kW 400 V [142 A rated].

Comparing NEC Table B.310.15(B)(2)(8) with IEC60364-5-52 Table A.52-5 (52-C4)

NEC 2 AWG[33.63 mm^2]161 A IEC 35 mm^2 144 A

The calculation theory are close: Nehrer&MacGrath vis-a-vis of IEC 60287.

NEC exudes the fragrance of democracy :less theory more practical.

So, the IEC is close to theoretical results while the NEC it is more practical.

__________________
Julius
Register to Reply