NFPA 70 430.22(A) Branch-circuit conductors for a single motor, continuous duty, shall have an ampacity of not less than 125% of the motor’s full load current.So, Cable Ampacity > 1.25 x FLA x derating factors.
As far as I searched there is no 1.25 multiplier in IEC, Cable Ampacity > FLA x derating factors.
Is the above correct?, or there are some multiplier/margins for cable sizing as in the current project we are going use the cables which are manufactured according to IEC.