Anonymous Poster #1

Bypass Isolator

02/08/2018 10:37 PM

Dear Sirs,

In case of double busbar schemes - both busbars are energized. But in case of main and transfer bus scheme - only one busbar is energized normally.

Is 'bypass isolator' used only in case of main and transfer bus schemes?

Regards,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Bypass Isolator.

02/08/2018 10:52 PM
Reply
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Bypass Isolator.

02/09/2018 12:09 AM

..."The bypass isolation switch is designed for applications where maintenance, inspection and testing must be performed while maintaining continuous power to the load. This is typically required in critical life support systems and standby power situations calling for safe system maintenance with no power disruptions."...

Bypass isolation switches are just alternative paths to provide uninterrupted power to critical systems during repair or maintenance of existing switchgear...sometimes they are part of a system to switch to an alternative power source such as in the case of emergency backup power when a power outage is sensed the switch is automatically triggered...

http://www.eaton.com/Eaton/ProductsServices/Electrical/ProductsandServices/ElectricalDistribution/ANSINEMAPowerDistributionandControlSystems/ATS/BypassIsolationTransferSwitches/ContactorBypassIsolationTransferSwitches/index.htm#tabs-3

https://testguy.net/content/256-6-Common-Substation-Bus-Schemes-Every-Test-Tech-Should-Know

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply Good Answer (Score 2)
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#3

Re: Bypass Isolator.

02/09/2018 5:50 AM

'Bypass' refers to bypass of the feeder CB.

When this is done, the transfer bus CB acts as the feeder CB, with all the subject feeder protection trips transferred to the transfer bus CB.

This is seen in Main and Transfer bus as well as Two main and transfer bus schemes.

This arrangement was popular when the outdoor CBs needed more/frequent attention.

__________________
Raghunath
Reply