DG set rating calculation

12/08/2005 8:24 AM

Pradeep writes:
Let me know how to calculate DG set capacity for a given motor load. The calculation must include voltage drop limit at the time of starting the motor.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Dec 2005
Location: Willenhall, UK
Posts: 159
#1

dg motor starting

12/09/2005 7:29 AM

for squirrel cage motors kva (g) = 0.42 x a x motor kw where a = 7 for dol starters, 2.5 for star delta starters, 3 to 4.5 for auto-transformer or invertor starters, 1.5 for slip-ring motors with resistance starters for slip ring motors with high starting power factor kva (g) = 1.12 x motor kw For multiple motor starting assume biggest is to be started first. eg 3 motors m1,m2,m3 whose size increase relative to there numerical value, then kva (g) = kva m1(running) + kva m2 (running) + (X x 0.42 x kw m3

__________________
A day without a smile is a day lost
Reply
Anonymous Poster
#4
In reply to #1

Re: dg motor starting

09/15/2006 1:02 AM

What should be the value of X given in the formula for multiple motor starting ?

Reply
Anonymous Poster
#12
In reply to #4

Re: dg motor starting

05/08/2010 12:41 AM

What should be the value of X given in the formula for multiple motor starting ?

Reply
Anonymous Poster
#8
In reply to #1

Re: dg motor starting

11/22/2008 1:00 AM

what is the factor 0.42 ? can u clarify?

Reply
Power-User

Join Date: Dec 2005
Location: Willenhall, UK
Posts: 159
#2

dg motor starting

12/09/2005 8:34 AM

I forgot to mention previously that the figures I have given are based on 20 to 25% volt drop which should be ok for most switchgear coils but may be noticable on lighting installations and computers

__________________
A day without a smile is a day lost
Reply
Power-User

Join Date: Jun 2005
Posts: 394
Good Answers: 1
#3

DG Set Sizing

12/09/2005 11:23 AM

A rule of thumb is to limit the motors that start simultaneously to .5 hp per kW of generator capacity. So if it is a 200 kW generator, no more than 100 HP of motors can be started simultaneously (or 75 kW). In general a 40% drop in voltage will drop out a motor starter.

Reply
Participant

Join Date: Sep 2006
Posts: 2
#5

Re: DG set rating calculation

09/25/2006 4:51 AM

Marathon Electric has a great "FREE" genset cd-rom catalog that has an excelent genset sizing software program in excel included.

The sizing program takes into account NEMA rating of the motor, voltage, Hz, type of starting and if you're doing multiple motor starting or sequence starting.

I've found this program excellent over the years in sizing gensets in the rental market for customer's motor starting jobs, including sizing for very large motors using multiple paralleled gensets to get the desired skva.

Reply
Anonymous Poster
#6
In reply to #5

Re: DG set rating calculation

08/07/2008 10:09 AM

i read your message is it possible to email me the your excel file at email id mobin@ariestech.co.in

Reply Off Topic (Score 5)
Anonymous Poster
#10
In reply to #5

Re: DG set rating calculation

10/08/2009 7:44 AM

How can calculate the capacity of a Dg set required if various loads including motors are given? Specify the ratings required for various satrting methods of motors, like DOL , Star Delta and Auto Transformer.

Reply
Anonymous Poster
#7

Re: DG set rating calculation

09/08/2008 3:05 AM

for 71.00 KW how to calculate DG capacity

Reply
Anonymous Poster
#9
In reply to #7

Re: DG set rating calculation

12/16/2008 6:57 AM

lubrication oil filling calculation

Reply Off Topic (Score 5)
Anonymous Poster
#11
In reply to #7

Re: DG set rating calculation

02/25/2010 2:32 AM

71/.9=78.88 + 20% = 100KVA

Reply Off Topic (Score 5)
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#13

Re: DG set rating calculation

04/22/2013 5:05 AM

Dear Mr.Pradeep,

Several times, this topic is discussed. Pl. search in this Forum, you will get several replies.

Pl. refer the link below.

http://cr4.globalspec.com/search/sitesearch?do=show&sort=textmatchrank&srch=selection%20of%20capacity%20for%20DG%20set&srchobjs=t%2Cc&fs=12&order=asc

DHAYANANDHAN.S

Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#14

Re: DG set rating calculation

10/08/2013 3:51 AM

Dear Mr.Pradeep,

In addition to my Posting No.13, above,with a link detail, pl.refer the following link which gives more details.

https://app.box.com/s/6205bfbb7766fbb51890

This link is retrieved from my archives. I think this answers your quiery.

DHAYANANDHAN.S

Reply