VFD Chokes are Choking Me Out!

03/06/2018 3:18 PM

Hey guys

So can someone either explain this to me or shoot me alink with some good info. My searches have not yeilded anything interesting.

I would to know several things,

What is the fundamental different of an AC vs DC choke

Is it the same physical construction? And when someone puts the AC designation or DC designation in front they are implying what its doing?

Is it circular like a toroid? and why?

Now on to the real question.

I have been told by SEW drives that they put AC choked before line reactors to mitigate over voltage spikes.

Can someone tell me how a choke prevents against over voltage?

I know we are trying to block harmonics from big transformers with the line reactors but i am confused about this choke business and why i am commonly seeing the two in series together on SEW VFD,s

Thanks in advance

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9912
Good Answers: 1141
#1

Re: VFD Chokes are Choking Me Out!

03/06/2018 4:31 PM

A choke is an inductor, which acts as a low pass filter. It allows low frequency like dc to pass but blocks high frequencies like voltage spikes. (The shorter the duration of a signal, the higher the frequency components are.)

DC chokes cut off at a lower frequency than ac chokes. A toroidal ferrite core is an efficient design that provides a closed magnetic circuit. Two inductors in series (like two resistors) add together.

https://en.wikipedia.org/wiki/Choke_(electronics)

Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#2

Re: VFD Chokes are Choking Me Out!

03/06/2018 4:46 PM

Basically it is whether or not a choke can handle the heat loss from AC core losses and DC wire resistance flowing through it or just the AC current flowing through it. Because don't forget a DC bias can easily saturate many core magnetic fields. A completely core less choke has no magnetic material to saturate so it ideally handles both but is often impractical to fabricate. At least this is AFAIK.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Commentator

Join Date: Sep 2017
Posts: 76
Good Answers: 1
#3

Re: VFD Chokes are Choking Me Out!

03/06/2018 6:13 PM

Very interesting, looking forward to hearing more responses

Thank you guys for answering. Much appreciated.

Register to Reply
5
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: VFD Chokes are Choking Me Out!

03/06/2018 10:42 PM

They serve different functions, but offer similar solutions to ONE problem, harmonics. An AC line reactor goes AHEAD of the rectifier in a VFD, a DC bus choke goes BEHIND the rectifier after the DC is created. On the DC side, the primary function is to help smooth out the DC ripple that results from rectifying AC through a diode bridge. In an inductor, voltage cannot change instantly, it follows what's called an "inductive time constant". So a change in voltage can only take place at a prescribed rate, so many volts/second/second. So when those ripples in the DC hit it, the DC choke acts (as previously mentioned) as a low pass filter, smoothing out some of that ripple. Down stream of the DC choke are capacitors to finish the job. You COULD just use all capacitors, and some VFDs do. But ALL capacitors in the WORLD come from 3 Asian sources, regardless of how many different brand names they sell them under. Those same sources ALSO make VFDs, so they have a way of controlling a high cost component for all of their competitors. So decades ago, VFD mfrs based in North American and Europe, in order to avoid helping their Asian competitors compete against them, started using DC bus chokes, because they can make them cheaply themselves (copper wrapped around steel) and it allows them to use half of the Asian capacitors they would otherwise need.

A side benefit of that, and the one they want you to believe is the PRIMARY benefit, is that it ALSO reduces the harmonics that the drive creates, by slowing down the rise time of the pulsed current draw of the rectifier diodes. That is the SAME thing that an AC reactor does as well. So from a harmonic mitigation standpoint, a VFD with no inductor can have 80-100% I-THD, whereas a VFD with EITHER an AC reactor OR a DC bus choke will knock that down to 30-35% I-THD. Both together will drop it to 20-25% I-THD by the way. As a gross generalization, 20-35% I-THD is often not enough, but it depends on a LOT of other complex factors. But it IS better than nothing for sure.

The unsung added benefit of an AC Line Reactor though is in helping protect the drive from line transients. Again, the same inductive time constant is in play, meaning a steeply rising line spike cannot pass through the line reactor at the same rate, it is slowed down which means it is stretched out over a longer time (even though the energy will be basically the same). That helps avoid having the diode bridge components being damaged by the spike. In addition if the VFD is RUNNING when a line transient occurs, there is another potential risk to the rectifier, a severe current spike (di/dt). I=f there is a "ringing" transient, such as from a utility grid switching event, where the transient is not just HIGH, but also then LOW, and it drops lower than the Forward Conduction Voltage of the diodes, so the diodes that are supposed to conduct in that cycle do not. That means they are not contributing energy into the DC bus and since the bus has capacitors and the transistors are going to pull energy out of those capacitors to send to the motor, the caps are depleted of energy that is not being replaced. So when the line transient decays a cycle or two later and the diodes can conduct again, the caps recharge INSTANTLY, and do so by pulling current through the diodes AT THE RATE OF THE AVAILABLE FAULT CURRENT IN THE SYSTEM! So you get a HUGE spike in current draw for one or two cycles and it can be 10-20 X the current rating of the diodes, which can damage them. So the line reactor slows down and stretches out that ringing transient as mentioned, allowing the diodes to stretch out that current draw to recharge the capacitors. A DC bus choke, because it is AFTER the diodes, doesn't offer that same protection.

Torroids mentioned earlier were only used in very small VFDs, but since almost ALL small VFDs are now made in Asia (regardless of the name on the outside) they typically don't have DC bus chokes at all. Torroidal chokes however ARE used a lot in VFDs as common mode noise chokes. Another different application from line and DC bus chokes.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 5)
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#5

Re: VFD Chokes are Choking Me Out!

03/07/2018 12:12 PM

It sounds like you are having problems getting enough current. Is you voltage output suffering?

Harmonic current is supposed to be turned into heat inside the main step down transformers but sometimes a little gets transformed back out on the power lines where your power factor correction capacitors generally reside. Too much harmonic current can cause the power factor capacitors to burn up (literally on fire) because the harmonic content changes reactance and causes the voltage to increase. Just an interesting little observation. Weird but true.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#6

Re: VFD Chokes are Choking Me Out!

03/07/2018 12:27 PM

Oh, and to answer your questions more completely, a choke is just an inductor who's impedance: Z = Ldi/dt which also equals 2*Pi*f*L where f is the frequency. Harmonic current is the sum of the currents at each of the harmonics of 60 Hz (or 50 Hz in some places). The sum is subject to vector analysis so that some harmonics add while others subtract. The result can be severe overheating of a motor if the 3rd, 7th, and 11th harmonic is too large.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Associate

Join Date: Oct 2019
Location: BANGALORE. INDIA
Posts: 54
Good Answers: 1
#14
In reply to #6

Re: VFD Chokes are Choking Me Out!

04/20/2020 2:19 AM

Dear Mr. NotUrOrdinary Joe

I am not an Elec. Engineer (Mech. Engineering Graduate, with Post Graduate in Sugar Engg., but considerably picked up Elec.Engg.) and I want one doubt to be clarified/cleared by you/

During the year 2011, there was a serious problem of (4 nos., of 600 KW, 630 Volts, base speed 1000 RPM, VFD drives) and enormous over heating of the drives noticed and the internal components like control cards got burnt. The Design and supply of Motors with VFDs is a well known multinational supplier and their Engineers could not solve the problem.

They told that the Harmonics effect is very high and told that the Harmonic currents of 5th, 7th, 11th 13th and 15th orders getting added ARITHMETICALLY (not VECTORIALLY) and resuts in over heating even though additional air conditioners installed.

After 7 days they brought some components and fitted in the VFD panel and the problem was under control but normalcy not reached. I find this statement of the Elec.Engineer from the supplier’s side is quite contradicting that in an electrical circuit all the current or voltages be VECTORIALLY added which we studied during our college days. When I raised this issue he replied that the harmonic frequencies are different and the vectorial addition will not apply and it is arithmetical addition only.

You have referred in your posting No.6 which reads as “Harmonic current is the sum of the currents at each of the harmonics of 60 Hz (or 50 Hz in some places). The sum is subject to vector analysis so that some harmonics add while others subtract. The result can be severe overheating of a motor if the 3rd, 7th, and 11th harmonic is too large.”

Pl. enlighten on this subject about it is vectorial addition/Arithmetical addition of current in the Elec. Circuits

Other CR4 Members also can post their comments.

Thanks,

DHAYANANDHAN.S

__________________
DHAYANANDHAN.S
Register to Reply
Commentator

Join Date: Sep 2017
Posts: 76
Good Answers: 1
#7

Re: VFD Chokes are Choking Me Out!

03/08/2018 4:30 PM

What a great bunch of info

Im still a little confused but seriously, what a great bunch of replies here

One thing i want to clarify. My original question is in regards to the separate components both line and load side of the VFD. I am no talking about the actual components on the SCCR

What i am getting at is , im trying to understand why an engineer before me in my job in a drawing set of ours installed both a Line reactor and a "choke" on the line side PRE VFD

Then has nothing connected to the load side.

I have come across transients before on the line side and actually had an SCCR develop a L-L short from harmonics and blow it self to pieces. (No line reactors)

Or perhaps was the scenario mentioned above about depleted caps and then an instantaneous current surge.

Really interesting stuff here.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: VFD Chokes are Choking Me Out!

03/08/2018 7:08 PM

"What i am getting at is , im trying to understand why an engineer before me in my job in a drawing set of ours installed both a Line reactor and a "choke" on the line side PRE VFD"

A line reactor IS a "choke", so I'm confused by your statement of someone putting "both" on the line side of a VFD. That would be like saying there is a wire AND a conductor; they are two words for the same thing.

Unless perhaps there was a line reactor, PLUS a torroidal choke or ferrite bead choke, possibly to reduce CM (Common Mode) noise from passing up stream? It would have been unnecessary on the line side of the VFD, as CM noise is generally dealt with on the load side or the DC bus because it is created by the transistors firing, not the diode rectifier.

But maybe this was an old old drive? Or maybe an old old Engineer who had been used to old "Six-Step" thyristor based VFDs from 30+ years ago? Hard to say now.

Regardless the issue now would be that there is no point in having two reactors in series ahead of a drive, in fact the voltage drop that would create may interfere with the motor operation.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#9

Re: VFD Chokes are Choking Me Out!

03/09/2018 8:43 AM

I agree with JReaf that there is no point in having both a line reactor and another choke on the line side. But a larger line reactor would amount to the same thing anyway. It could be that the installed reactor is undersized, but it is more likely that your harmonics from other nearby devices is already near "critical mass". That is a tough call and hard to measure because harmonic currents tend to flow all around a network depending on what else is connected at that instant. Consequently, as things turn on and off, the harmonic current will seek its own path instantly as well.

All of that being said, it seems that few people are aware of a special version of transformer where a few windings are borrowed from an adjacent transformer to mitigate harmonics. In a three phase power system, three transformers are nearly always used but a special version can mitigate harmonics very effectively by mixing a little of the adjacent power onto the windings of a single phase transformer. That is a really cool trick and it apparently works very well. Leave the load side alone.

I only know of one vendor who does this, but there are others and this is an established method for calming down dirty power. You can email me directly through clicking on my pseudo-name for further recommendations.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Commentator

Join Date: Sep 2017
Posts: 76
Good Answers: 1
#10

Re: VFD Chokes are Choking Me Out!

03/09/2018 10:01 AM

ah ok

i see what your saying

Here is some more info then

Ill give you guys the part numbers and links and maybe you can tell me what the difference is.

Everything is SEW and this is an SEW MoviTrac system

They had an upstream breaker then

SEW # ND045-013

on page 255 they call this one a "LINE CHOKE"

Here but go to page 255

Then continuing in series again PRE VFD they put a

SEW NF048-503

Click Here to see

Then the VFD

Then a motor disconnect and finally the motor

So if what you guys say is correct that a choke is a Line reactor what is SEW talking about

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#13
In reply to #10

Re: VFD Chokes are Choking Me Out!

03/09/2018 8:00 PM

OK, the NF 0480503 device is what's called an "EMC Filter", EMC stands for Electro-Magnetic Compatibility, a requirement for power electronic devices that are used in IEC conforming countries in order to attain CE compliance. But yes, that device does ALSO have a choke / reactor inside, along with other components, but is designed strictly for high frequency emissions, i.e. EMI/RFI radiation into the surrounding environment. That one has nothing to do with protecting the VFD or reducing harmonics.

You don't indicate where you are, but if you are in North America, that device is totally optional. If you are basically anywhere else, it may not be.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#11

Re: VFD Chokes are Choking Me Out!

03/09/2018 10:28 AM

Take a look a this link, http://www.es.eaton.com/HMT/ (sorry, link no longer available) or harmonics mitigating transformers. It would be preferable to too many chokes. Each inductor reduces the available line voltage as well as increasing the power factor load. A transformer, on the other hand, deals with the issues directly but it will be a more expensive solution.

Too much inductance from chokes or line reactors (different names for a series inductor) will make it hard to charge up the capacitor bank in the VFD. That DC voltage in the capacitor bank is the power source from which the VFD recreates a synthetic voltage at the desired frequency. If it suffers from "Low Voltage" it will disable the VFD.

Your fix might be as simple as removing the additional line reactor but it may also be a matter of replacing the VFD. Removing the line reactor may destroy the VFD and then you will be able to buy one that matches up with your motor. By the way, the motor manufacturers have a certain type meant to work at "other" frequencies via a VFD. Pairing up the two is always best.

Upgrading other DC power supplies is also a way to remove harmonics. The type used in computers changed years ago to low harmonic content designs. But very few other DC supplies have been treated the same. Harmonic current also burns up neutral lines in a three phase system. If you read the frequency on the neutral, you are likely to find the fundamental frequency is the 3rd harmonic. No surprise for us EE types. Most of the time the problems are created within the facility.

Just use your favorite search engine with these magic words, "Mitigating Harmonic Distortion".

Lastly, click on the "Rating" box and apply "Good Answers" for those you feel were helpful. Good luck with your issue.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Sep 2017
Posts: 76
Good Answers: 1
#12
In reply to #11

Re: VFD Chokes are Choking Me Out!

03/09/2018 10:43 AM

Thank you very much sir

What a great bunch of info here. I hope this thread also helps others learn more about this topic. I wish they taught more of this in school honestly. Im a recent grad in my second year of work so still struggling to learn all the applications of the basics taught in EE.

You guys have been very helpful to the new engineer.

Register to Reply Score 1 for Good Answer
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dhayanandhan.s (1); JRaef (3); NotUrOrdinaryJoe (4); redfred (1); Rixter (1); scott165 (4)