Transformer Test

04/04/2018 1:38 AM

dear all

in DC resistance test for power transformer(off load T.CH) when value of resistance for one phase is different.now how we can discriminate the fault in winding transformer or in tap changer.and which test limit the fault in winding or tap changer

thanks

Register to Reply
Pathfinder Tags: transformer test
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Associate

Join Date: Mar 2017
Posts: 41
#1

Re: transformer test

04/04/2018 2:30 AM

Such a very nice information about the transformer testing.

__________________
Power Transformers in India | Wire Assembly Manufacturers in India | Transformer Manufacturer in India
Register to Reply Score 2 for Off Topic
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Transformer Test

04/04/2018 9:27 AM

Well this is a case where the actual numbers found will very much matter to the diagnosis. Since you provide us not even a sample...

If you anticipated 100 ohms and you found 1.7 million ohms then you have a break in the wire. If instead you found 0.2 ohms then you have a short circuit. If instead your number varies less than the expected tolerance percentage from the magnet wire manufacturer then get over it.

Now how to discriminate between a tap wiring mistake and a transformer winding mistake using only a DC resistance check it still helps to have actual numbers. I find a sketch of what and how one is testing a circuit also helps immensely. Well it does for one capable of testing for a simple mesh analysis.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Transformer Test

04/04/2018 10:35 AM

You must work with coolyar.

Ask the manufacturer how he did it!

Read these and LEARN SOMETHING!

Guide to Transformer Resistance Testing

Transformer Winding Resistance Test

Measuring DC Winding Resistance of Transformer

Register to Reply
Guru
Popular Science - Cosmology - Let's keep knowledge expanding Engineering Fields - Retired Engineers / Mentors - Hobbies - HAM Radio - New Member

Join Date: Dec 2006
Location: North America, Earth
Posts: 4528
Good Answers: 106
#4

Re: Transformer Test

04/05/2018 11:37 AM

Your question is a little unclear. Are you asking how to test for a faulty transformer or to test for the wrong tap being selected or what? I built a 60Hz ohmmeter to use for testing transformer phase and other problems. It used 60Hz rather than DC, so faults are easily identified (impedance at 60Hz is much higher than DC resistance). There are LCR bridges that can do this type of measurement.

__________________
“I would rather have questions that can't be answered than answers that can't be questioned.” - Richard Feynman
Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

kumarpradeep (1); lyn (1); redfred (1); StandardsGuy (1)

Previous in Forum: Island Mode Operation   Next in Forum: Small Synchronous Motors

Advertisement