Island Mode Operation

04/01/2018 5:14 AM

can a coal based power plant unit operate in island mode ? the question is related keeping in view the physical process limitation of steam generation to cope up with load variation in island mode.say a coal unit of 40MW supplies a load of 22MW ( 6MW being house/aux load of the unit).now if the load suddenly increases to 30MW, then i think the generator will trip on low freq and voltage.this is because the process of coal to steam generation is inherently slow.sufficient time is taken to increase coal feed rate,to generate increased steam from increased coal fed. the trip times of protections would have been timed out before steam is increased.what you guys think?

regards,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: island mode operation

04/01/2018 8:40 AM

I'm sorry but this sounds like an unrealistic question. 15% of your power generation capability goes to running the power plant that has a total load of 55% capacity. Then suddenly, all at once and unexpectedly faster than operators can anticipate, a single 20% load gets added to make the load to make 75% of capacity. You think this prohibits a coal/steam power plant from operating in island mode. Well when any power plant encounters a change in loading greater than the reserve capacity, thus a load change that can damage equipment, then relays are supposed to protect the infrastructure (generator, transformer, cables). If clueless operators forget to stoke the fires prior to the morning surge in demand then yes, ESO should demonstrate the deficiency of the operators.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Island Mode Operation

04/01/2018 11:08 AM

I think that you should hire someone who has experience with the dynamics of steam plant operation, the analysis that is required goes far beyond handbook-engineering and/or back of the napkin calculations.

First you have to know whether the plant's control and protective relaying systems will even allow standalone operation, so the answer would be "NO" unless the governor/turbine control/protective relaying systems are specifically designed for such operation.

If they are, then you have to know all the settings including such things as time constants, delays, gains, etc. for the governor, fuel/burner management, steam valve, and excitation control systems, as well as the dynamic characteristics of the T/G and the proposed loads.

Once you have that (and much more) data then you can start doing prefault/postfault transient stability analyses of your system.

Not all units perform well (if at all) when sudden loads are applied. Been there, done that, having performed many highly instrumented live-system tests to verify that the computer models accurately reflected what really happens in real life.

btw- Island operation usually refers to a grid connected unit that suddenly finds itself tripped from the rest of the grid. Is that the case here or is the unit designed for supplying only local load with its own frequency reference source?

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jul 2011
Posts: 286
Good Answers: 1
#4
In reply to #2

Re: Island Mode Operation

04/01/2018 11:59 AM

i agree with what you said.the unit is basically designed for operation in grid connected mode.however the national grid is unstable and usually trips.we do not want our coal unit to trip and want it to operate in off.grid or isolated mode to supply our local load. now i think that coal based units cannot operate in isolated/off grid mode

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: Island Mode Operation

04/01/2018 6:42 PM

Then how did the first such unit ever manage to operate at all?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Jul 2011
Posts: 286
Good Answers: 1
#7
In reply to #5

Re: Island Mode Operation

04/02/2018 10:16 AM

can you prove that first ever unit operated was coal based? (niagra falls?)

Register to Reply Off Topic (Score 4)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #7

Re: Island Mode Operation

04/03/2018 2:43 AM

No responder to any thread needs to prove anything.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6
In reply to #4

Re: Island Mode Operation

04/01/2018 9:14 PM

This engineering science not political science; what you think is irrelevant, what counts is how the plant is designed and the load that it is supplying.

While it is true that there are lags inherent in the coal handling system, there are much shorter loops that may carry the plant through a momentary upset out on the grid, dependent of course on the nature, magnitude, and duration of the upset.

A 40MW unit running at 55% might easily handle a short term 34% step change in its output if it is designed for load-following operation; however, only someone with complete expert knowledge of the dynamics of the unit can determine what "short term" and "momentary" mean in the context of the unit/load of your particular situation.

Sorry, guesswork doesn't work for me...

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Island Mode Operation

04/01/2018 11:14 AM

There is a magic feature of the internet that can be used by the uninformed to gather limited knowledge about most any subject.

It is also very fast, compared to wasting time asking anonymous strangers to provide the information that you seek. That is just half fast.

It's called a search engine.

What is meant by the island mode operation of a power plant? - Quora

sland mode operation feature - Decentralized Energy

Island operation | DEIF

Improving the Flexibility of Coal-Fired Power Plants - Power Engineering

Don't be half fast. Do some research for yourself!

Register to Reply
3
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#8

Re: Island Mode Operation

04/02/2018 3:24 PM

Sure, go ahead, there is no problem here running a coal power station in islanded mode with massive load swings.

Given your previous questions on CR4 perhaps this will finally get you fired.

See my responses to your previous questions. Sadly I don't believe this is an April Fools day joke.

Based on your previous posts I am not confident you should try as I don't believe you have the necessary education and training to perform such a delicate and dangerous job.

I would strongly advise other professionals to do the same. I view your continued questions on CR4 to allow you to perform your job as unethical on multiple levels.

__________________
jack of all trades
Register to Reply Good Answer (Score 3)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9
In reply to #8

Re: Island Mode Operation

04/02/2018 4:51 PM

I agree. There comes a time when personal safety should overrule the free dispensation of knowledge not possessed by the requester.

Especially to those who continually display a lack of competence.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#10

Re: Island Mode Operation

04/02/2018 11:29 PM

they used to build steam accumulators, back in the olden days, rather large ones.

This upset scenario doesn't sound like a show stopper, voltage is a function of field excitation, not necessarily rotational speed, most load devices have a pretty wide frequency tolerance, so might not be as bad as you think. Usually not bad enough to warrant stopping the whole show.

Not much reason to trip the generator on low voltage or frequency, except when that shows as a precursor of unrecoverable power system collapse or external fault exceeding the current rating of the windings, long term or short term.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12

Re: Island Mode Operation

04/03/2018 2:46 AM

<...what you guys think?...> is irrelevant.

This is a question of design. And the only CR4 subscriber that can see the original design documentation is the Original Poster.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13

Re: Island Mode Operation

04/03/2018 3:23 AM

So:

  • Why is low frequency or low voltage a trip-worthy problem in <...Island Mode...>?
  • Is there a high frequency or high voltage trip?
  • What are the current trip settings during <...Island Mode...> operation, and are these realistic/problematic? Why?
  • If the thing trips, then 30MW goes off-line; of what consequence is this for the plant?
  • What happens when the unit becomes disconnected from the local grid and an 8MW load gets applied to it - don't the commissioning records say at all? What operational experience is there of this scenario?
  • Were these scenarios ever written into the original Commissioning Plan document for testing? If not, then why not?

The documentation that answers these questions cannot be seen from here...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#14

Re: Island Mode Operation

04/03/2018 8:14 AM

Dear Mr.coolyar,

The details given by you is insufficient.

Before going to the subject, the load increase resulting in higher steam demand involves several parameters. As we all know, that it depends upon:

1. The Heat Release Rate in the Furnace and its control.

2. The Degree of Pulvarisation of Coal.

3. The Percentage Constituent of the Pulvarised Coal i.e., Percentage of different particle size in Microns or MM.

4. The Air-Fuel Ratio.

5. The Moisture in the Coal.

6. The calorific Value of Coal.

7. Actual Non-Combustibles in the Coal

8. Less Furnace Temp. on account of higher Excess Air.

9. Less Temp. of Pre-Heated Air.

10. Less Feed Water Temp. entering the Boiler Drum.

11. Higher percentage of combustible particles in the ash (partly relating to Heat Release)

12. Higher percentage of Carbon-Monoxide than permissible.

13. Insufficient Draught, actual draught – not asper manufacturers recommendation.

14. Excessive gap ID Fan Impeller guide cone where lot of recirculation takes place, thus reducing the quantity of actual capacity of Flue Gas sent out of Boiler.

15. Excessive gap of FD Fan Impeller guide cone where lot of recirculation takes place, thus reducing the quantity or actual capacity of air pumped in to the Boiler.

16. Excessive gap of SA Fan Impeller guide cone where lot of recirculation takes place, thus reducing the quantity or actual capacity of air pumped in to the Furnace.

17. Higher slippage of ID Fan, FD Fan Belt, reducing the capacity of the Fans, thus less air.

You have to furnish the following details.

1. Do you have a bunker at the top – to store pulvarised coal for a minimum of 8 to 10 Minutes of duration for full capacity of Power Generation.

2. What is the Excess Air% used. Is it asper Boiler Manufacturer’s Manual.

3. What is the analysis of CO2 % and O2% and CO% in the Flue Gas.

4. What is the % of combustibles in the Ash Collected.

5. What is the Percentage of Non-Combustibles in the Coal.

6. What is the Calorific value of the Coal.? Is it with in the limits specified.

7. What is the Moisture% of Coal

8. What is your Grid Voltage.

9. What is the pulvarised coal particle sizes in Percentage.

Regarding Tripping due to Grid related issues – the Transmission Line Voltage has considerable impact for stable operation. Higher the Voltage, more the stability.

DHAYANANDHAN.S

Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

coolyaar (2); dhayanandhan (1); jack of all trades (1); lyn (2); PWSlack (3); RAMConsult (2); redfred (1); rwilliams (1); Tornado (1)

Previous in Forum: Treat Meter's Service Disconnect as Main Panel?   Next in Forum: Transformer Test

Advertisement