Background:
My brother, who lives in Massachusetts, has a home with a 'standalone' meter with an adjacent 200A service disconnect, which feeds a ~100ft run to his house.
I've created these setups myself for mobile homes in Oklahoma, but normally we do it as follows:
1. Three wires enter the meter box from the utility - 2 hots and 1 neutral.
2. Three wires leave the meter box and enter the service disconnect box which is about 12" away.
2. The two hot wires go to the 200A service disconnect. Two hot wires then leave the disconnect.
3. The neutral wire connects to a bus next to the service disconnect, which is 'earthed' via a ground rod (or two), and then two wires leave this bus, one is neutral, and a new 'ground'.
4. Ultimately, we end up with 4 wires leaving the service disconnect, and from that point forward neutral is never bonded to ground, and no more ground rods are driven even at sub-panels.
Now, as far as I know, what I described above is 'standard' - you simply treat the first panel as the 'main' and treat anything downstream as a subpanel.
My brother's setup is very different though...

1. FOUR wires enter from the utility (left side). One is obviously a ground.
2. TWO wires enter the meter. The neutral and POCO-supplied ground simply bypass the meter and go to the service disconnect box (also about 12" away).
3. The POCO ground connects to the neutral bus in the service disconnect box, but there is no 'customer side' ground rod or 'earthing' conductor.
4. THREE wires leave the service disconnect box and go to the house - 2 hots and 1 neutral.
5. The panel in the house 100ft away has an 'earthing' conductor to a ground rod, and neutral and ground are bonded in that panel. So, basically, the service disconnect is 'ignored' as a panel and the house panel is treated as the main panel.
Here are my questions:
A. Is my brother's setup okay? If so, is this the kind of thing that varies by jurisdiction?
B. If not, it would seem to me that we need to treat the service disconnect as the 'main panel' and the following needs to happen:
- Drive a couple of ground rods near the service disconnect and ground the neutral bus
- Run a fourth 'grounded' conductor to the house.
- Un-bond neutral from ground at the house's panel and disconnect the ground rod there (basically, treat it as a sub-panel).
- [I'm not worried about the neutral going right to the bus as the meter doesn't do anything with it anyway, and the meter socket might not even have neutral lugs - I haven't seen it so I don't know]
Other notes:
I should also mention the following two things:
- Apparently, his setup did pass inspection at one point, so that's a tick in favor of saying it's okay.
- However, the conductors leaving the 200A disconnect are 1/0-1/0-1/0 aluminum, which is obviously undersized. To be fair, the house's main breaker is 100A, but it still seems sketchy to me as the wire isn't protected between the disconnect and the house. So, I'm not 100% confident the inspector really paid attention(??)
Thoughts very much appreciated!