I need to know if I can get this kind of 3 ph. transformer:
Primary 138kv
Secondary 13.8kv/25kv
The idea is the hydro uses 13.8kv for distribution voltage, but in the future there is a consideration to move the distribution voltage to 25kv. I am wondering if this would be possible with out changing the power transformer, if we get the transformer that would have a secondary 13.8 and 25kv voltages. Currently we will use 13.8 and in the future upgrade the cables and use 25kv.
Good Answers: 445
Re: Transformer
03/30/2018 2:51 PM
Without knowing the ratings, impedances, and vector group of the transformer and the system/protective relaying to which it will be connected; it's only a guess.
Re: Transformer
03/30/2018 4:01 PM
Sorry not to give some details
size 30/40/50 MVA
Z%=7.5
DY1
solidly grounded
Good Answers: 131
Re: Transformer
03/30/2018 2:52 PM
The best way to determine that is to contact some transformer manufacturers. You don't say where you are located in the world, but there are multiple manufacturers of large power transformers, and they probably have done something like that. You also don't tell what rating the transformer must be (kVA or MVA size) and if the windings should be delta or wye configuration. I have seen smaller power transformers that have reconfigurable secondary windings that allow multiple voltages. However, there may be capacity limitations at some of the voltage taps - that's something to discuss with the manufacturer. I suspect it mostly depends on how much you are willing to pay...
Re: Transformer
03/30/2018 3:03 PM
You can maybe just add a step-up transformer....
Good Answers: 42
Re: Transformer Question
03/31/2018 11:42 PM
You said:
"Currently we will use 13.8 and in the future upgrade the cables and use 25kv."
It seems to me you have already your 138/13.8 kV transformer. For the future if you'll need any way another transformer order a standard 138/25 kV one. This will be cheaper I think.
If the future means over 10-15 years then you will need a new transformer, probably.