PRV Question

03/30/2018 12:06 PM

Dear all,

Good day.

The (Pressure relief device) in transformer operated, and we made (Dissolved

gasses analysis) & (oil break down) test, and the result its ok.

The question is do we have to check the isolation or just check the dissolved gases.

Thanks for all.

Register to Reply
Pathfinder Tags: PRV
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: PRV

03/30/2018 1:05 PM

You should follow your local codes or whomever is the Authority Having Jurisdiction (AHJ). CR4 has no authority or jurisdiction over anyone, anywhere. If you desire us to translate into English the reasoning of the AHJ, that we might be able to help.

If I were the AHJ and I knew more about the type of transformer in question I might say just purge and pressurize with inert Nitrogen and put the transformer back in storage. Then again I might declare the transformer as now scrap metal, buy a replacement. There are also a myriad of other intermediate options involving hi-pot testing, oil replacements, among other things.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: PRV

03/30/2018 1:09 PM

You have to determine why the PRV operated before you re-energize the transformer.

Did something bump into the tank, was there any switching/lightning in the area, was the PRV defective, did any other protective relaying operate, do you have any prefault DGA to compare with, is there a TDR that caught the misoperation, have you compared the insulation resistance readings with the previous tests, have you done an oil BDV test, any particulate matter/water in the oil, etc., etc.

Contact a trained professional, especially if the transformer is a critical asset.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#3

Re: PRV

03/30/2018 1:29 PM

Once we had PRV operation on a transformer in our plant. It was because the conservator was isolated.

When the transformer was returned to service after maintenance, the personnel forgot to open the isolation valve in the pipe connecting the transformer tank to the conservator.

As we know when the transformer is loaded, the rise in temperature causes oil to expand and there was no way to go as the conservator is isolated.

You may like to check.

__________________
Raghunath
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#5
In reply to #3

Re: PRV

03/30/2018 3:50 PM

Still you should seek your AHJ. We are not your AHJ.

If you are hoping to put this transformer into operation at the very least you must verify that the PRV is the only thing that vented when it was over pressured. If coolant or liquid insulation (oil) is allowed to drip out you may produce a bigger disaster than just an oily floor.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4

Re: PRV

03/30/2018 2:46 PM

The pressure relief is only there to tell you that some event took place that produced excessive pressure. You have to determine what that is. Certainly your oil tests, if they were done correctly, should help you know whether that "event" that took place was an arc or other fault in the oil. But the only way to be sure your transformer is in acceptable condition to put back in service is to do a complete battery of tests to verify that all the major systems (windings, insulation, bracing, etc.) are good.

I would recommend that you find a good, independent high voltage testing company that can do this, preferably one that is a member of the InterNational Electrical Testing Association (NETA - see www.netaworld.org). They should conduct tests per the "Standard for Maintenance Testing Specifications for Electrical Power Equipment and Systems" published by NETA, which will include such tests as:

  • DC Insulation resistance
  • DC winding resistance
  • Turns ratio test
  • Doble Insulation Power Factor or dissipation factor test

These can tell you whether the transformer has experienced a fault that compromises its ability to be put back in service. Don't gamble on something that is probably the largest single cost in your substation.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

PeterT (1); raghun (1); RAMConsult (1); redfred (2)

Previous in Forum: Looking for LED Strip Fixture for a Warning Light   Next in Forum: Transformer Question

Advertisement