Grounded Field Winding

04/30/2018 10:14 AM

dear all

I know the first ground fault in the field winding is signalizing only,because a single

earthing in the field winding is not immediately damaging,but why the

protection wait to second ground fault to trip the generator why not trip in the first

ground fault.and what should be do if the signal (field grounding) appear

thanks

Register to Reply
Pathfinder Tags: field winding
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Grounded Field Winding

04/30/2018 10:35 AM

Well, that would depend upon the contents of the detailed electrical design documents with regard to any neutral connection, which documentation cannot be seen from here.

If there were no neutral to <...ground...> connection, then the first fault would not cause damage, though it might prove inconvenient, embarrassing, uncomfortable, or some combination of them. A guess might suggest that having two parts of the <...field winding...> both connected to <...ground...> would introduce heavy circulating currents through those connections and the <...field winding...> that might damage things considerably, and it would be better to trip on the fault than for the damaging situation to continue for longer than the trip operating time.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Grounded Field Winding

04/30/2018 8:44 PM

When I was an engineering student on a co-op assignment at a major generating station, I posed the same question to my manager. His answer was simple and perfectly logically, "Continuity of service". Rather than an immediate trip which would suddenly remove 600MW of generation from service, the operators were alerted to the ground fault, and could perform an orderly shutdown of the unit without affecting any customers.

My followup question was obvious, "what about a second ground fault?". His answer, "It's unlikely that a second fault will occur before we take the unit out of service, but if it does, we're already prepared for the trip."

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#3

Re: Grounded Field Winding

05/01/2018 11:23 AM

One ground fault may or may not let out the magic smoke eventually depending on where the fault occurs.

Two ground faults are guaranteed to let out the magic smoke in the very near future.