Delta versus Wye

09/13/2007 3:08 PM

If you were to connect a motor in delta configuration to a 347volt-3phase system would it have the same power output if it were hooked up in wye configuration to 600volt 3 phase??

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Delta versus Wye

09/13/2007 7:40 PM

Yes, provided your motor is wound for that.

AND you find a 347V 3 phase system someplace!

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: May 2007
Location: Budapest, Hungary, HA5YAR
Posts: 617
Good Answers: 14
#2

Re: Delta versus Wye

09/14/2007 3:14 AM

Yes.

__________________
Aged man is not old man...
Register to Reply
Power-User

Join Date: Mar 2007
Location: Bangalore, India
Posts: 141
Good Answers: 1
#3
In reply to #2

Re: Delta versus Wye

09/14/2007 3:47 AM

Yes. Energy consumed would be same irrespective of input voltage excepet some small losses.

__________________
Best Regards, Shivaram
Register to Reply
Associate
New Zealand - Member - New Member

Join Date: Aug 2007
Location: Christchurch, New Zealand
Posts: 39
Good Answers: 1
#4
In reply to #3

Re: Delta versus Wye

09/16/2007 6:18 PM

Yes, provided that the voltage across the windings is the same, and the frequency is the same, there will be no difference. NB the line voltage is root three higher for a star connection to keep the same winding voltage as delta connection. If the frequency changes, change the winding voltage by the same ratio as the frequency change.

Best regards,
Mark Empson
http://www.LMPhotonics.com | http://www.LMPForum.com

Register to Reply