I am wondering if I am missing something obvious so new eyes might help.
I am looking at some pre ITB (Invitation to Bid) documents for the custody metering run for an LNG import and regassification station.
The LNG is pumped up to pipeline pressure and then vaporised. It then goes through a custody metering run (ultra sonic meters are specified). Downstream of the meter a relief valve (PSV) is shown.
The piping is 30", 900# rated with a normal operating pressure of 100barg
The site is in Colombia but there is general reference to API / ASME standards
There is no description to give the basis for the PSV so this all becomes deduction and assumption.
As the system is essentially piping I would not expect to provide over pressure protection except in a few cases.
In cold liquids thermal valves are provide to allow for venting trapped liquids that have warmed.
In some designs of gas metering stations there was a pressure let down vlave upstream of the meter run to set constant pressures for the meter to improve accuracy. There is no pressure reduction in this case.
As the pressure is provided from a pump I would expect the piping to be designed for the shut in head of the pump or if not for any over pressure protection to be at the pump.
Fire. Vessels are normally protected against overpressure due to fire but not piping. Although the meter run has large volumes I believe (I know a dodgy assumption) that it will all be constructed to piping code.
So I do not think any of the usual reasons would apply in this case. Having (correctly) selected 900# pipe class the design pressure could be up to 150barg so it sould be possible to set the DP in line with the pump shut in head.
I am thereby perplexed as to why this PSV is in place. Any thoughts would be welcome