HVAC Unit Outputs

06/27/2018 12:35 AM

I'm Installing an HVAC unit that has a 2-10 vdc output to control a Hot water mixing valve . However there is no relay output to start pump to supply the hot water.

Could someone suggest a simple, economical way to make a 120vac pump start (with a relay) when the mixing valve control voltage hits 2.1 volts. Thereby running the pump only when it is actually needed.

Thanks for any suggestions.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: HVAC Unit Outputs

06/27/2018 12:49 AM

Is this another test question?

Voltage Regulator Circuit

Register to Reply
Associate

Join Date: Jun 2016
Posts: 29
#5
In reply to #1

Re: HVAC Unit Outputs

06/27/2018 11:23 AM

No.

Register to Reply
Guru

Join Date: Oct 2014
Location: Hemet, Land of milk and honey.
Posts: 2365
Good Answers: 36
#6
In reply to #1

Re: HVAC Unit Outputs

06/28/2018 2:06 AM

Lyn, I'm sure you know that IHAICI, has seminars that cover this subject, among others.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: HVAC Unit Outputs

06/27/2018 12:55 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: HVAC Unit Outputs

06/27/2018 4:17 AM

Google "trip amplifiers", and select one that suits the Client's specifications.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#4

Re: HVAC Unit Outputs

06/27/2018 5:17 AM

As already given in replies, "trip amplifier" is what you want, for 120VAC supply, 2-10 or 0-10 VDC input with a relay output suitable for 120VAC.

Usually the output relay is not suitable for switching a motor, words like "resistive load" qualify the volt/amp rating. You have not given motor rating or current.

So you will probably also need a motor starter relay or assembly, perhaps with coil spark suppression to avoid spark interfering with trip amp.

Motor starter relay will have to comply with local standard CSA/UL/EN/IEC/VDE for size of motor, which may require an approved assembly like an enclosed starter with isolating switch & overcurrent protection.

Register to Reply Good Answer (Score 2)
2
Power-User

Join Date: Jun 2012
Posts: 123
Good Answers: 7
#7

Re: HVAC Unit Outputs

06/28/2018 5:36 AM

You can install an auxiliary end-switch on your mixing valve that makes contact when the valve starts to open and breaks contact when the valve has closed.

These switches are low-priced and suitable for 120VAC pilot duty. Check with the manufacturer/dealer of the valve.

Register to Reply Good Answer (Score 2)
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

67model (1); lyn (1); PWSlack (1); REH (1); SolarEagle (1); tonyhemet (1); Zvi (1)

Previous in Forum: AC Resistance vs DC Resistance   Next in Forum: Modbus RTU 485

Advertisement